Schneider MPPT 60-150 has output current but input shows as 0A
jacksond
Registered Users Posts: 3 ✭
i have just installed two Schneiders MPPT 60-150 charge controllers, charging a 430AH 48V battery. Thr battery appears to be charging ok but the readings on the charge controller display are not consistent with meter readings taken with a clamp on meter. The input voltage (112v) is recorded correctly by the charge controller, but the current and power are shown as zero, whereas clamp on meter shows ~7A at 112v. The output readings are also inconsistent. The charge controller readings for current and power as half that recorded at the output by the clamp on mete. I am seeing the same thing with both charge controllers. Any ideas what might be causing this anomaly?
Comments
-
Part of that output could be going to running loads while the batteries are getting only a portion of the total output. When your charge cycle is in absorb or float mode the batteries are only using a portion of the full solar output, running loads are using power right from your solar panels.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
If you connect the panel negative lead directly to the charger's negative lead, you bypass the internal current shunt.
Most other controllers have the shunt in the positive circuitry and don't care which negative controller connections are used.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
jacksond said:...two Schneiders MPPT 60-150 charge controllers, charging a 430AH 48V battery...
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
I am guessing that you do not have the XW or new SW inverter/chargers? They supply the data of the load and even though you can get alot from the mppt's, the inverters really are needed to give you all the charts, grapghs, and display data and ease of using this system.
You do have the SCP at minimum right? You would need to power it from the AUX output or an external 12V source. This would then make a network and all the settings would be global."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Thanks for all the suggestions. Turns out I had the PV negative lead connected to the battery negative bar in the PDP rather than going directly to the charge controller input. Corrected that and now everything is as expected.
-
You also need to remove the 1 amp fuse in the 2nd controller or the ground fault wont work correctly.
XW6848 inverter with 2 X mppt 60 150 CC , with Canadian solar 260Watt panels 2 x 3.5 kw array
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed