Problem with Solar Generator
Comments
-
Going 24v makes sense.
Have you run a true capacity test on your batteries lately?
I would expect your particular battery bank when fully charged, to hold something like 12.1v to 12.3v running under a 150 amp load.
AT a 50% state of charge, a 150 amp load should pull you down to about 11.8v to 11.9v.
I am wondering if higher resistance connections are a problem in your system.
I would start by removing the threaded-in SAE size post adapters from the batteries. Those are designed for automotive cable ends. You should be connected directly using the the same 8mm stainless bolt supplied, to land your cables right on the terminals.
When you unscrew the automobile post adapters, you will see that you will be getting about 3-5 times the surface contact area for your lug-to-battery connections.
I always have more questions than answers. That's the nature of life. -
Marc Kurth said:Going 24v makes sense.
Have you run a true capacity test on your batteries lately?
I would expect your particular battery bank when fully charged, to hold something like 12.1v to 12.3v running under a 150 amp load.
AT a 50% state of charge, a 150 amp load should pull you down to about 11.8v to 11.9v.
I am wondering if higher resistance connections are a problem in your system.
I would start by removing the threaded-in SAE size post adapters from the batteries. Those are designed for automotive cable ends. You should be connected directly using the the same 8mm stainless bolt supplied, to land your cables right on the terminals.
When you unscrew the automobile post adapters, you will see that you will be getting about 3-5 times the surface contact area for your lug-to-battery connections. -
Putting it as a question: Why are you using the automotive posts on the batteries right now?
You should just unscrew the brass "SAE automotive" adapter posts from the batteries. You don't want them there, they are working against you.
Once you have removed them, just attach your existing cable right to the battery, in the same threaded socket that the adapter post was screwed in. You will immediately that this gives you a much larger metal-to-metal contact area.
The female thread in the battery housing is 8mm. The thread where you are currently connected on top of the brass post is 8mm.
Use the same bolt, the same cable, same location - just take the extra piece out for a better connection.
That brass post adapter comes with the batteries for people that are using automotive type cables.
You are not using automotive cable ends and don't want them on there without a good reason.
I always have more questions than answers. That's the nature of life. -
Marc Kurth said:Putting it as a question: Why are you using the automotive posts on the batteries right now?
You should just unscrew the brass "SAE automotive" adapter posts from the batteries. You don't want them there, they are working against you.
Once you have removed them, just attach your existing cable right to the battery, in the same threaded socket that the adapter post was screwed in. You will immediately that this gives you a much larger metal-to-metal contact area.
The female thread in the battery housing is 8mm. The thread where you are currently connected on top of the brass post is 8mm.
Use the same bolt, the same cable, same location - just take the extra piece out for a better connection.
That brass post adapter comes with the batteries for people that are using automotive type cables.
You are not using automotive cable ends and don't want them on there without a good reason. -
OK, that makes sense now!
I can assure you that the brass automotive post adapters are removable. They have their own 8mm stud on the bottom. They are removable specifically for the reason discussed. (I have put a LOT of Fullriver batteries on industrial/commercial/mobile systems)
The hardware looks stock, just as Fullriver normally ships. The stainless bolt on top is not as long as the post adapter - it only goes down about half way. So your bolt will not change. The batteries were designed with the same bolts/threads for interchangeability with and without the SAE post adapter.
Edit to add picture - I took this for you to see what I mean. This is a larger battery, but the concept is the same:
I always have more questions than answers. That's the nature of life. -
Thanks Marc, I had no idea. Honestly though, the guy that put my solar system together was more on the solar grid end of things so I guess he had never worked with too many battery systems. I sure have found out a lot about my unit through this forum. Alway's good to find ways to make improvements
-
Raj174 said:Here's a better price, new, free shipping, and a Google trusted store.
https://www.universalmania.com/products/xantrex-freedom-sw3024-inverter-charger-3000w-24v?variant=26324533511&gclid=CNjQ6vDe0s4CFQkMaQodZkYCSA
This is the spec doc on the unit.
http://www.xantrex.com/documents/Inverter-Chargers/Freedom-SW-24V/DS20160505_FreedomSW24V.pdf -
Hey Guy's,
Have a dumb question. When you order the xantrex freedom sw3024 is it necessary to order the control panel separate or is it possible to adjust the charge rate downward (from 75amp to 55amp) without it? It looks like the control panel is another $175 or so -
lc0338 said:Raj174 said:Here's a better price, new, free shipping, and a Google trusted store.
https://www.universalmania.com/products/xantrex-freedom-sw3024-inverter-charger-3000w-24v?variant=26324533511&gclid=CNjQ6vDe0s4CFQkMaQodZkYCSA
This is the spec doc on the unit.
http://www.xantrex.com/documents/Inverter-Chargers/Freedom-SW-24V/DS20160505_FreedomSW24V.pdf4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
lc0338 said:Hey Guy's,
Have a dumb question. When you order the xantrex freedom sw3024 is it necessary to order the control panel separate or is it possible to adjust the charge rate downward (from 75amp to 55amp) without it? It looks like the control panel is another $175 or so
I think this info is available at www.xantrex.com4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
lc0338 said:When you order the xantrex freedom sw3024 is it necessary to order the control panel separate or is it possible to adjust the charge rate downward (from 75amp to 55amp) without it? It looks like the control panel is another $175 or so
I have my inverter in the garage, but my controls are in the house. If controls were built-in to my inverter, I would have had to buy 2 sets of controls (the built-in and the remote). Also, many folks stack several inverters to make split phase or three phase power... if each of the inverters had built-in controls, they would have had to buy several sets of controls.
You do need to control your inverter. Buy the controls. Exception, maybe... There is a trend toward network (computer) control of electronics. I'm not too familiar with Schneider, but maybe you can control it with a laptop computer.
--vtMaps
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
lc0338 said:Raj174 said:Here's a better price, new, free shipping, and a Google trusted store.
https://www.universalmania.com/products/xantrex-freedom-sw3024-inverter-charger-3000w-24v?variant=26324533511&gclid=CNjQ6vDe0s4CFQkMaQodZkYCSA
This is the spec doc on the unit.
http://www.xantrex.com/documents/Inverter-Chargers/Freedom-SW-24V/DS20160505_FreedomSW24V.pdfSchneider Electric Conext SW 4024 3,500 Watts, 24VDC Inverter/Charger for Split-phase 120/240 VAC
$1,495.00
Or the 2524 for $1250"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
vtmaps said:lc0338 said:When you order the xantrex freedom sw3024 is it necessary to order the control panel separate or is it possible to adjust the charge rate downward (from 75amp to 55amp) without it? It looks like the control panel is another $175 or so
I have my inverter in the garage, but my controls are in the house. If controls were built-in to my inverter, I would have had to buy 2 sets of controls (the built-in and the remote). Also, many folks stack several inverters to make split phase or three phase power... if each of the inverters had built-in controls, they would have had to buy several sets of controls.
You do need to control your inverter. Buy the controls. Exception, maybe... There is a trend toward network (computer) control of electronics. I'm not too familiar with Schneider, but maybe you can control it with a laptop computer.
--vtMaps
It looks like when advertising the inverter/charger it would be made a little more evident that the control panel needs to be ordered, if first time use, and give a part number. I could have overlooked it though. -
Well, Thanks to all for the input. I pulled the trigger and placed an order. Got an email a few minutes later from my credit card provider if I recognized these purchases. I had bought some gas earlier for my diesel truck so it was 50+ dollars and placed the order for the inverter/charger for $1930 and then there was one other transaction (at walmart) that was declined.... it turns out my wife went to walmart after work and tried to check out a little while after I placed the large inverter order and they declined HER card. I guess I will be spending the night in the dog house. I was going to keep this purchase quietXantrex 25' Network Cable for SCP Remote Panel × 1 - $29.68Xantrex Xanbus System Control Panel (SCP) for Freedom SW2012 3012 × 1 - $174.45Xantrex Freedom SW3024 Inverter Charger - 3000W - 24V × 1 -$1,726.27shipping free
from universal mania -
Xantrex makes an SW 2024 (2000W continuous, I think 3000 peak), it's only about $300 cheaper but it will fill your needs. The big problem with the 12V system at those outputs is that 125 amps is a lot for that weight of batteries, and requires 2/0 cables to not have an issue with transmission losses even across comparatively short runs.
It's the kettle that's really the issue. Maybe look for one that runs at a lower wattage? 900 or so would be easy to work around. Might make more sense than trying to beef up a system that is otherwise working for you.
Edit: And then I read to the bottom and see you already pulled the trigger. Well, it should work fine for you, let us know. -
DRickey said:Xantrex makes an SW 2024 (2000W continuous, I think 3000 peak), it's only about $300 cheaper but it will fill your needs. The big problem with the 12V system at those outputs is that 125 amps is a lot for that weight of batteries, and requires 2/0 cables to not have an issue with transmission losses even across comparatively short runs.
It's the kettle that's really the issue. Maybe look for one that runs at a lower wattage? 900 or so would be easy to work around. Might make more sense than trying to beef up a system that is otherwise working for you.
Edit: And then I read to the bottom and see you already pulled the trigger. Well, it should work fine for you, let us know. -
Any shading at all on a series string can cause a considerable drop in PV output.4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset.
-
You'll probably take less of a hit running them in parallel at a less than ideal voltage for the MPPT controller than in series for only two panels. I ran my pair of 235W both ways, with similar mobility making it difficult to control shading, and found that overall, I was better with parallel.
The MPPT is going to be stepping it down either way, it's just not quite as efficient with a single panel's worth of voltage. And in the long run, you'll probably make up in the inverter side what you're losing on the charging. -
DRickey said:You'll probably take less of a hit running them in parallel at a less than ideal voltage for the MPPT controller than in series for only two panels. I ran my pair of 235W both ways, with similar mobility making it difficult to control shading, and found that overall, I was better with parallel.
The MPPT is going to be stepping it down either way, it's just not quite as efficient with a single panel's worth of voltage. And in the long run, you'll probably make up in the inverter side what you're losing on the charging. -
What you have are called grid tie panels, and you definitely need 2 in series to charge a 24 volt battery with a MPPT controller.4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset.
-
I'm not sure what the issue is, other than that at a Vmp of 30.9 he's right on the margins for equalizing batteries. But he can plugin and equalize with the charger/inverter every few months to fill that gap, which is better than having his charging drop through the floor because a whip antenna or power line is shading a panel.
-
Try it both ways, it's just a wiring configuration change. If the parallel config doesn't work for you, reconfigure.4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset.
-
on fullriver agm battery website it states that if batteries are properly charged they do not require equalization: here is a statement i copied and pasted:
Refresh Charge
If Fullriver batteries are properly charged they should never require an equalizing charge. If they were not properly charged and there is a decrease in capacity, recharge the batteries and make sure they complete the entire charge cycle. If the batteries are stored for extended periods of time, recharge them as follows:
-
Yeah, as I understand it AGM batteries don't need equalizing, in some cases it can actually damage them. In liquid-electrolyte cells it is used to stir the electrolyte and remove impurities from the plates.
-
AGMs, while they are not supposed to need equalization--Some "equalization" can be done by extended charging times at normal absorb voltage.
Here it is--A "conditioning" charge for Concorde:
http://www.concordebattery.com/Chairman_Technical_Manual.pdf
Note that other brands of AGM batteries may not tolerate this high of charging/recovery voltage.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
BB. said:AGMs, while they are not supposed to need equalization--Some "equalization" can be done by extended charging times at normal absorb voltage. Here it is--A "conditioning" charge for Concorde:
By the way, the popular Iota battery chargers are sometimes used (on the grid) to hold batteries at float voltage. When used that way, they do an automatic weekly "equalization". The "equalization" is really just a normal absorb cycle at absorb voltage. Its purpose is to break up the stratification that occurs during float in flooded cells.
--vtMaps
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
AGM batteries can/do get unbalanced over time (much less than flooded cell batteries). And doing longer than normal absorb charging once every 6-12 months has been a recommendation (by at least some folks) for a number of years now.
The AGM conditioning to "recover capacity" with higher than normal (absorb) voltage is (as far as I know) for Concorde batteries only.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
@BB: I completely agree on both points, Bill.
Doing an occasional extended absorb run, really helps bring the cells back in line with each other. I am also convinced that getting a 10-12 hour float charge occasionally, really helps the process.
I have recovered a huge amount of storage capacity, from abused Concorde batteries via equalization at 2.6v per cell for 8 hours, per their recommendation.
One recommended method to help recover from extended deep discharge sounds extreme, but has worked well to breathe new life into batteries that appeared ready for recycling:
Charge at a constant current of 5% of the the C20 rating, until voltage rises to 2.6v per cell. Then continue at the same current for another 4 hours, which may require as high as 3.0v per cell. Terminate and wait for cool down if battery exceeds 130 F. This process should only be performed starting from a fully discharged condition.
All AGM batteries are not the same.
Marc
I always have more questions than answers. That's the nature of life. -
Well, have received the xantrex 3000 watt 24 volt inverter charger. Hoping to get it installed within the next few days. I'll get a picture once everything is installed. Going to have to do some re-arranging inside the cabinet due to the larger size inverter.
-
just a quick question for those familiar with the xantrex 3024 inverter charger.
in my solar generator I have a battery disconnect switch to turn on/off the inverter. It does not look like this new inverter charger will allow that. Is buying the remote the only option to turn on/off other than the remote. I would like to turn it on/off without taking the front door off. I plan to call xantrex cust support but they are on pacific time and its early here and also sometimes the wait time is long. Thanks for any quick response.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed