Solar Expert Posts: 177 ✭✭✭
Hi...sorry...BB...VTmaps.......DAVE!??? anyone?
So I launched this bank 2 days ago.
I set all the charging parameters according to the Deka recommendations. Both on the CC and the charger for the Generator.
Bulk max = 30% of C20
Absorb = 58.8
Float = 56
Equalize = 61.2
First day I got it all "charged up"...more or less...well... until it was into float and ran an EQ to get the cells SG's closer together. Batteries started pushing my comfort level for temps (80F) so I stopped the EQ after 3 hours. SG was getting things closer across all the cells at this stage. (When I first hooked it all up they were all over the place) Yesterday the sun got it through to float. Checked the SG across all the cells. Some where high some were low. 1.300 on the high side and 1.250 on the low end. 1.265 was about the norm.
As per the instructions I did an EQ to get the cells closer together. Ended up 1.300 on the high end and 1.265 on the low. Ok...
Cloudy day today. I start up the genset...it bulk charges...absorb charges...kicks into float...at 98% SOC
The CC is reading bulk charging...and remember I have the charging settings identical between the CC and the remote at this stage.
Checking the SG gives me readings in the 1.275 on the high end and 1.250 on the low.
So do I keep trying to EQ things...check something? Change something?
How do I send beer across the internet?
So I launched this bank 2 days ago.
I set all the charging parameters according to the Deka recommendations. Both on the CC and the charger for the Generator.
Bulk max = 30% of C20
Absorb = 58.8
Float = 56
Equalize = 61.2
First day I got it all "charged up"...more or less...well... until it was into float and ran an EQ to get the cells SG's closer together. Batteries started pushing my comfort level for temps (80F) so I stopped the EQ after 3 hours. SG was getting things closer across all the cells at this stage. (When I first hooked it all up they were all over the place) Yesterday the sun got it through to float. Checked the SG across all the cells. Some where high some were low. 1.300 on the high side and 1.250 on the low end. 1.265 was about the norm.
As per the instructions I did an EQ to get the cells closer together. Ended up 1.300 on the high end and 1.265 on the low. Ok...
Cloudy day today. I start up the genset...it bulk charges...absorb charges...kicks into float...at 98% SOC
The CC is reading bulk charging...and remember I have the charging settings identical between the CC and the remote at this stage.
Checking the SG gives me readings in the 1.275 on the high end and 1.250 on the low.
So do I keep trying to EQ things...check something? Change something?
How do I send beer across the internet?
11.5 kw array - 3 - midnite solar classic 200's - Magnum MS-PAE Inverter - Magnum ME-RC50 remote - ME-BMK batt-monitor - 2 simpliphi lithium (48v) - Yamaha ef3000ise - 1 confused look on face
Comments
-
And can I even do an EQ if only one of the two says it is in float?...well I know I can do it...but is it wise?11.5 kw array - 3 - midnite solar classic 200's - Magnum MS-PAE Inverter - Magnum ME-RC50 remote - ME-BMK batt-monitor - 2 simpliphi lithium (48v) - Yamaha ef3000ise - 1 confused look on face
-
It may take 25-50 cycles before your batteries achieve their full capacity and SG. --vtMaps
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Your Batteries are new, in 20-50 full cycles the plates will be fully formed and the SG's will level out and become consistent. You can keep on doing EQ's and they will be off again after the first cycle.
-
...hahaha...well...they should probably put that in big ol' bold letters somewhere!
hahaha...they probably do...but my ADD and dyslexia often win this battle.
Ugh.
Thanks everyone!
11.5 kw array - 3 - midnite solar classic 200's - Magnum MS-PAE Inverter - Magnum ME-RC50 remote - ME-BMK batt-monitor - 2 simpliphi lithium (48v) - Yamaha ef3000ise - 1 confused look on face -
You have done nothing wrong, it's perfectly normal to do an equalizing charge when commissioning a battery bank, some battery companies recommend it!Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Photowhit...thanks...and thanks to everyone else.
All valid points!
Actually....A big shout-out to everyone on the forum in the last few weeks who have donated thoughts on any of my dumb questions.
I have learned a lot.11.5 kw array - 3 - midnite solar classic 200's - Magnum MS-PAE Inverter - Magnum ME-RC50 remote - ME-BMK batt-monitor - 2 simpliphi lithium (48v) - Yamaha ef3000ise - 1 confused look on face -
morpho said:
Cloudy day today. I start up the genset...it bulk charges...absorb charges...kicks into float...at 98% SOC
The CC is reading bulk charging...and remember I have the charging settings identical between the CC and the remote at this stage.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed