Solar Expert Posts: 36 ✭
I have four us2200xc6 volt batteries giving me 12 volts 450 amp hours
I'm trying to find the specs for all charge rates,max charge ,float,etc.
I have not been able to find it . Any help gets a big Thank You
Rene
I'm trying to find the specs for all charge rates,max charge ,float,etc.
I have not been able to find it . Any help gets a big Thank You
Rene
Comments
-
Re: Batteries
Google can't find that string [ us2200xc6 ]
So you should have a mgf name & model # on the batteries.
Rule of thumb, normal charge rate, about 10 % of rated AH, so 45A charger would likely be safe.
Our Host, wind-sun has a battery page http://store.solar-electric.com/batteries.html
and a deep cycle battery FAQ http://www.windsun.com/Batteries/Battery_FAQ.htm that has some of the info in it, but really, the battery Mfg has the last say on the specs you seek.
The first thing , is what style of battery are they, Flooded (with fill caps on top) AGM, Gel, or what ?? They battery type does influence the voltages at different charging stages, if a sealed AGM battery was to be charged like a flooded cell, it would be destroyed in a few weeks.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: Batteries
it would appear they have a high absorb voltage by the pdf here from the manufacturer. each 6v battery fully charged = 7.75v or more and for 2 in series or 12v systems it's 15.5v or more.
http://www.usbattery.com/usb_images/warr_chart_2008_a.pdf
they don't specify a float voltage and that you can email them for, but i'd suspect around 6.75-6.9v. multiply by 2 for 12v.
btw the ah 20hr capacity is 232ah for your battery so in parallel this creates 464ah. -
Re: Batteries
From the US Battery Website:(typed manually from img file)- C/10 charge current (20 Hour rate AH Capacity)
- Charge until 2.583 per cell (7.75@6v, 15.50@12v)
- Hold voltage for 2 to 4 hours then stop charging.
- Charge time = 10 hours
- Reduce charge voltage by 0.028 volts per cell for every 10F above 80F, increase voltage by same amount for every 10F below 80F.
- Float: 2.17 volts per cell (with above temp adjustments--13.02 volts for floating a "12 volt" battery bank)
Their sizing recommends multiply AH requirement by 2.4x... 2x (50% max discharge), +20% (for aging). Don't discharge below 1.200 specific gravity.
Typed in the information to make it easier to fine in Wind-Sun forum when searched.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Batteries
Thanks everyone
Neil your correct on the amp hours I just like the number 450 I guess. -
Re: Batteries
banjorene,
you're welcome and you might want to double check with the manufacturer on these voltages as it goes from very high absorb to a bit low on float imho.
bb,
i missed that float voltage spec and that in general seems low to me. most controllers may have difficulty going that much of a spread between absorb and float as many are limited to up to 2v like blue sky or the xantrex c series that don't have the ability to go over 15v on absorb, but can float at 13v. -
Re: Batteries
Niel,
Yea--every vendor seems to have its own spin on charging/maintenance...
Sounds like US Battery likes to charge "hard" (pretty much an equalization/stirring charge every cycle) and then float at just above the "full charge" level of the battery... Will use a bit of water when charging--but probably hardly anything when floating/storage... When the battery is "put back into service" after a winter's float--probably would not hurt to run a charge cycle through it first.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed