these are the loads to be powered by the GRID-TIED PV SYSTEM
CKT LOAD DESCRIPTION VOLT VA AMPERE PROTECTION
1 HALLWAY LIGHTS 220 1500 6.82 20
2 HALLWAY LIGHTS 220 1500 6.82 20
3 HALLWAY LIGHTS 220 1500 6.82 20
4 GS AREA LIGHT 220 1500 6.82 20
5 GS AREA LIGHT 220 1500 6.82 20
6 GS AREA LIGHT 220 1500 6.82 20
7 LP PENT-B/6 (GSAL) 220 1500 6.82 20
8 DATA CENTER 220 1500 6.82 20
9 CONVENIENCE OUTLET 220 1260 5.73 20
10 E. DINING LOUNGE 220 1800 8.18 20
TOTAL CONNECTED LOAD 68.47
TOTAL KVA 15060
IL = 68.47 Amperes
USE : 2-22mm²THHN & 1 - 8.0 mm² in 32mm Ø
Main : 100AT, 150AF, 2P 240V 2-WIRES, 60Hz, 25 KAIC C.B.
these is our calculations on the system
Power Calculation
SUNTECH STP280-24/Vb Xantrex GT3.3 = 3300Wp
Wp: 280 W Total # of Inverters: 5
Voc: 44.8 V
Vmp: 35.2 A
Isc: 8.33 V
Imp: 7.95 A
# of Modules in Series: 10
# of Modules in Parallel: 2
# of Modules in Series: 11
# of Modules in Parallel: 3
Total number of Panels to be used: 53 pieces
Maximun Power @ STC (Pmax): 280 W
Total Power Generated: 14,840 W
Current Calculations
PV SOURE CIRCUIT:
1. Calculating for Maximum Circuit Current
PV Maximum Circuit Current : 10.4125 A
Cable/Conductor and Overcurrent Device Ampacity Rating : 13.015625 A
Overcurrent Device Rating : 15 A
PV OUTPUT CIRCUIT:
PV Maximum Circuit Current : 52.0625A
Cable/Conductor and Overcurrent Device Ampacity Rating : 65.078125A
Overcurrent Device Rating : 75 A
http://s278.photobucket.com/albums/kk108/wildshot_photo/?action=view¤t=53panel5inverters.jpg
did i missed something?... and is this correct the connection to the grid we made
I am not that confident about this design, any comments, suggestion regarding this design are appreciated
TOTAL KVA 15060
IL = 68.47 Amperes
Power Calculation
Voc: 44.8 V
Vmp: 35.2 A
Isc: 8.33 V
Imp: 7.95 A
PV SOURE CIRCUIT:
PV OUTPUT CIRCUIT:
Re: comments/suggestion are appreciated in here
Not quite sure what your loads represent ...
As for the PV side, you should consider using less inverters, my system is about 12kW and I use a pair of Xantrex GT5.0 and one GT3.3
Your generation will be about 50-70kWhr day depending on the time of year
Also, on a residential service, having a second breaker panel attached to the meter is not something I have seen before and the electric company and or city/town building department might have something to say about that
What are you trying to do and what is your location? -
Here is a website that may assist you with load sizing calculations, chose any battery, and calculate the KWH from the final results. What you didn't show clearly, is the amount of time each load will be on.
Here for battery sizing: (javascript required)
http://www.freesunpower.com/battery_designer.phpPowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
good day sir, I live here in Manila Philippines...
sir regarding the supply side connection i just followed the supply side connection from the articles of code corner MAKING THE UTILITY CONNECTION FOR LARGER SYSTEM by: JOHN WILES
thank you sir for the advice
sir sorry for the the drawing I was'nt able to give some of the info, the panel is not the main panel. its a lighting panel for the 3rd floor of the building.
the meter is a submeter for the 3rd floor who occupies it...
I am trying to design a GT PV system (no battery backup)... i just maximize the area of the the roof where the array is to be placed. 53 panels can suit the allowable area for the solar panels...
regarding the loads sir its 17721watts 12 hrs/day all for lightings
and 2 other convenience outlet...
thank you sir
have a productive day
walang_problema