can i tie two power inverter together?
indercool2004
Registered Users Posts: 1 ✭
both the off grid power inverters are same make and same output 300watt , 10A MPPT each , i have 2 solar panel of 100w. I would like to tie both the inverter together at AC side to make 600 watt inverter. is it possible ?
Re: can i tie two power inverter together?
Certain inverters are made for stacking like that. Most are not. Connecting most inverters in parallel will result in one or both burning out. It is a matter of having to match the output frequency.Northern NM, 624 watts PV, The Kid CC, GC-2 batteries @ 24 VDC, Outback VFX3524M -
Grid tie inverters (GTIs), on the other hand, do not require anything special to parallel since all of the inverters will sync themselves to the grid voltage frequency and phase.
When stacking stackable off-grid inverters, you may still need a transformer if your intention is to produce 240V from two 120V inverters.
Some inverters' stacking capability even allows you to run them 180 degrees out of phase to produce a balanced 240 without using a transformer.SMA SB 3000, old BP panels. -
From the OP's other thread, here is more detail:
The answer to the question for those specific models would have to come from the manufacturer, although the manuals for the two may contain the answer.[we have] Trace Inverter SW4048. Our local solar company happens to have a SW5548 laying around.SMA SB 3000, old BP panels. -
Unless they are specifically built to be tied together (stacked), they have no way of syncing their output waveforms, so you will end up with a 4th of July style display until things settle down and the smoke clears. -
So the question becomes whether those two specific Trace models were built to be stackable. I do not have the answer. Does anyone else out there?waynefromnscanada wrote: »Unless they are specifically built to be tied together (stacked), they have no way of syncing their output waveforms, so you will end up with a 4th of July style display until things settle down and the smoke clears.SMA SB 3000, old BP panels. -
Re: can i tie two power inverter together?waynefromnscanada wrote: »Unless they are specifically built to be tied together (stacked), they have no way of syncing their output waveforms, so you will end up with a 4th of July style display until things settle down and the smoke clears.
I was going to say that !!Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
Re: can i tie two power inverter together?From the OP's other thread, here is more detail:
The OP only has one post on this forum.
Welcome to the forum Indercool2004,
Your power inverters at 300 watts, 10 amps, with MPPT must be what are called "microinverters". They are meant to be used one inverter per solar panel in a grid-tie system. Is that how you intend to use them?
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i
- 231 Forum & Website