grid-tie on a detached garage?
System
Posts: 2,511 admin
Hello all - nice forum you've got here.
I'm looking at putting a new roof on my detached garage and I'm thinking about doing a grid-tie solar system there while I'm at it.
The garage is currently wired for power with a 240v single phase circuit from the 200 amp main panel going to a small 2-breaker panel in the garage.
My question is - can I do the grid-tie into the garage circuit(without tearing up my yard for new wiring), or do I have to run new wires into the main panel, or does the grid tie have to live between the main panel and the meter?
Thanks for any input.
I'm looking at putting a new roof on my detached garage and I'm thinking about doing a grid-tie solar system there while I'm at it.
The garage is currently wired for power with a 240v single phase circuit from the 200 amp main panel going to a small 2-breaker panel in the garage.
My question is - can I do the grid-tie into the garage circuit(without tearing up my yard for new wiring), or do I have to run new wires into the main panel, or does the grid tie have to live between the main panel and the meter?
Thanks for any input.
Comments
-
Re: grid-tie on a detached garage?
hi PORTLAND, Or INTERNETWORKS (If you don't tell us where you are, we have to track you down - Europe does use a 240 single phase, 50hz)
How do you get your 240 V single phase ? Most of the US uses a 120V split phase, and between the 2 split phases, you can get 240V
If your sub panel has capacity to add 2 more 15 A breakers ( one on each phase ), and your main panel can handle it, you should be OK.
BUT the Electric Co. may want an accessible cut-off at the main meter, they don't want to have to dig around looking for the solar breakers.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: grid-tie on a detached garage?
It depends on the size of your branch circuit to your garage... For example, If I recall correctly, for a 125 amp service to your garage, you will be able to run a 20 amp breaker to your solar system--or a maximum of about 240vac*20a*0.8=3,840watts...
For a residential system, you can only run a maximum of ~20% (I am sorry, I don't recall the exact number) of your utility service/sub-panel breaker for your solar system. And you can only run a circuit at a maximum of 80% of its rated capacity. For a commercial building--IIRC, basically, add up all the breakers and subtract from rated capacity of the panel.
So, depending on your sub-panel size in the garage will define how large a system you can have before you have to rewire and dig up your yard.
Also, in most places, the utility requires a easy to get to solar disconnect switch--typically somewhere near your meter is the best place. If you have dogs/etc. that limit access--that will be an issue.
Lastly, if, for example, your utility feed is on your house, and the garage is some distance away and you don't have a 125+ amp panel in the garage (you would have to rewire the panel)--you also have the option of placing the panels on the garage and trenching the DC solar cables to your home and installing the inverter/disconnect there and wiring to your main distribution breaker box (or put the panels/inverter on the garage and run the 240 VAC circuit back to the home)... This would probably be the better solution--you will save a lot on copper wire / installation since you will not be running a large branch circuit/sub-panel to your garage... Just enough copper to support the solar system.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: grid-tie on a detached garage?hi PORTLAND, Or INTERNETWORKS (If you don't tell us where you are, we have to track you down - Europe does use a 240 single phase, 50hz)
How do you get your 240 V single phase ? Most of the US uses a 120V split phase, and between the 2 split phases, you can get 240V
If your sub panel has capacity to add 2 more 15 A breakers ( one on each phase ), and your main panel can handle it, you should be OK.
BUT the Electric Co. may want an accessible cut-off at the main meter, they don't want to have to dig around looking for the solar breakers.
Sorry, Portland Oregon, PGE customer.
Exactly what you said, split phase. I believe the 240v breaker on the subpanel is 50A, so if I'm calculating correctly that's 960w? Which is actually a fair sized setup if I'm not looking to do battery-based off grid operation - correct me if I'm wrong?
My subpanel may not have space for two more breakers, however I could expand it.
Now what's this about a cutoff? Does it have to cut the solar specifically or couldn't the cutoff work on the entire main panel if the need arises?
I realize I should probably start a different thread for this, but I was thinking about doing a metal roof and the thin-film solar material that comes in long rolls? Sorry I'm not totally up to speed on the terminology yet... any comments on this idea?
Thanks again. -
Re: grid-tie on a detached garage?
PG&E is one of the (few?) utilities that may not require you install a lineman accessible disconnect.
Regarding the sizing of the system, 1kW is on the small size for a grid tied system... 3kW seems to be a sweat spot for the best $$$/watt pricing.
Also, check your metering laws... In California, we have to use E6 Time of Use metering... A small grid tied system on a home where people use a lot of power (especially afternoon/evening)--adding a small grid tie system can actually cause your electric bill to be higher (because of the rate plan penalties for afternoon/evening use).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: grid-tie on a detached garage?
690.64 (B)(2)
The sum of the ampere ratings of overcurrent devices in circuits supplying power to a busbar or conductor shall not exceed 120 percent of the rating of the busbar or conductor.
My interpretation - which has been agreed on by one inspector anyway
All breakers that supply current must add up to 120% or less of the busbar/enclosure rating of the panel. Generally, this will just be the main and the breaker for the PV. If the panel/busbar are rated for 125 amp then the total of main + PV breakers must be less than or equal to 150 amps.
This could mean a 125amp main and a 25 amp PV breaker or it could be a 100 amp main and a 50 amp PV breaker.
Also, BB, when you calculated the max power - 240Vac*20amp*.8 - why * .8?
Your max AC power should be 240Vac*20amp(in that example) = 4800W AC
and 4800W AC / .8 = 6000W DC
no? -
Re: grid-tie on a detached garage?
NewEnergy,
Your explination sounds like the correct interpretation--the intent is to keep everything safe--and your method, as far as I can tell, does meet the intent.
Also, if there are sub-panels involved--those same questions need to be asked/answered for upstream breaker panels too...690.64 (B)(2)
Also, BB, when you calculated the max power - 240Vac*20amp*.8 - why * .8?
Your max AC power should be 240Vac*20amp(in that example) = 4800W AC and 4800W AC / .8 = 6000W DC
no?
The assumption is that NEC will only let you install permanent loads (fixed installations vs plugs like wall outlets) up to 80% of the branch circuit rating...
For example, a 15 amp branch can only have 15a*0.8=12 amp wired load...
So, my assumption is that would be true going back the other way--the solar generation source can only drive 80% of the branch circuit's current rating (one could argue 240 vs 220 VAC in the formula--Grid Tied inverters are constant power devices... As the AC Mains voltage falls, the output current rises--to keep P=I*V=constant).
The issue is that you have two devices that limit current/power... One is the solar panels themselves--but they are not very accurate and the sun/weather does not always perform as expected... So while 3,500 watts of solar panels are PTC rated around 3,000 watts (including inverter losses)--on cold bright days, with a little cloud/snow reflections, the panels can exceed their ratings... However, in my case, my inverter is also limited to 3,000 watts maximum by design--so even if I have larger panels, the inverter will not pass more energy.
Jim/Crewzer is the expert at the NEC ratings/deratings... It works out that the max current the circuit has to be designed for is something like 1.25 (1/0.80 for NEC branch circuit rating) times 1.25 (allow for solar panel safety factor) = 1.5625 wiring up-rating over solar panel expected output.
There are other discussions that we have gotten into here before about NEC's sometimes a bit crazy rules for solar charge controllers / Grid Tied inverters that some of us don't agree with--but that is for another post/thread.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: grid-tie on a detached garage?
Oh yeah, Continuous load, forgot about that. I just thought the .8 was a deration of the PV output. -
Re: grid-tie on a detached garage?
Just so there's no confusion, the original poster seems to be on PGE (Portland General Electric), not PG&E (Pacific Gas and Electric).
If there's already a service panel in the garage, I see no reason why the solar couldn't be grid-tied at that point.
Be sure to check the insolation maps for your area. I lived in Beaverton for a while, and seem to recall there was a lot of cloudy and foggy weather. Maybe climate has changed, that was decades ago. -
Re: grid-tie on a detached garage?Maybe climate has changed, that was decades ago.
How could the climate change ?
--
global warming - ever since the last ice agePowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed