Issues with AIMS inverter/charger
ckhd
Registered Users Posts: 4 ✭
Hello everyone,
I have a co-worker who recently bought an AIMS PICGLF30W24V120V 24v 3KW inverter/charger with a built-in MPPT charge controller. He is having a terrible time with it.
I have not laid eyes on the system (he lives 30 miles out of town), but I do have 25 years experience with PV (my Dad's off-grid systems). I have had him test and try everything. He has 1.6KW in panels, and four L-16 batteries. It is all hooked up correctly (even the people at Northern AZ Wind & Sun, where he bought the inverter, say it's right).
My boss also has several years of PV experience (he lives off-grid and I helped him with his initial PV system choices). He has not laid eyes on the system either, but also believes it is all connected and set up correctly.
His problem is that his batteries do not charge well. He comes home from work (with the inverter being off all day and 10+ hours of nice AZ sun) and his batteries are in the low 24v range (verified charge state with a hydrometer). So, he fires his generator every evening to charge the batteries. They charge fine on the generator (charged state also verified with a hydrometer).
I have read every page in the manual, and there are literally NO adjustable settings for the MPPT charge controller portion, other than a battery type selector (which is set correctly according to the manual). We've gone over the 'correct' settings in the manual and he has verified his inverter is set the way it should be.
I have never had any experience with AIMS equipment. My experience is mostly Trace, Xantrex and Outback.
After lengthy discussions with my co-worker and boss, I have decided it has to be one of the three following things:
What are your thoughts?
Do any of you have much experience with AIMS products?
Help!
Bowen
I have a co-worker who recently bought an AIMS PICGLF30W24V120V 24v 3KW inverter/charger with a built-in MPPT charge controller. He is having a terrible time with it.
I have not laid eyes on the system (he lives 30 miles out of town), but I do have 25 years experience with PV (my Dad's off-grid systems). I have had him test and try everything. He has 1.6KW in panels, and four L-16 batteries. It is all hooked up correctly (even the people at Northern AZ Wind & Sun, where he bought the inverter, say it's right).
My boss also has several years of PV experience (he lives off-grid and I helped him with his initial PV system choices). He has not laid eyes on the system either, but also believes it is all connected and set up correctly.
His problem is that his batteries do not charge well. He comes home from work (with the inverter being off all day and 10+ hours of nice AZ sun) and his batteries are in the low 24v range (verified charge state with a hydrometer). So, he fires his generator every evening to charge the batteries. They charge fine on the generator (charged state also verified with a hydrometer).
I have read every page in the manual, and there are literally NO adjustable settings for the MPPT charge controller portion, other than a battery type selector (which is set correctly according to the manual). We've gone over the 'correct' settings in the manual and he has verified his inverter is set the way it should be.
I have never had any experience with AIMS equipment. My experience is mostly Trace, Xantrex and Outback.
After lengthy discussions with my co-worker and boss, I have decided it has to be one of the three following things:
- The inverter/charger is set/programmed incorrectly
- The inverter/charger is faulty
- The inverter/charger is poorly designed
What are your thoughts?
Do any of you have much experience with AIMS products?
Help!
Bowen
Comments
-
Re: Issues with AIMS inverter/charger
I don't see any AIMS products on the Northern AZ Wind & Sun store.
What panels is he using? Sounds like it is not hitting the batteries enough.
Edit: the attachment shows your range of programming it looks like:
from http://www.aimscorp.net/documents/PICGLF30W24V120V.pdf -
Re: Issues with AIMS inverter/charger
As Solar Dave asks... What are the solar panels Vmp/Imp and how are they arranged?
Many people by "24 volt panels" which are actually Vmp~30 volts. In hot weather, you can see Vmp fall with temperature down by 20% to ~24 volts (plus wiring+controller voltage drop).
A "real" "24 volt panel" has rated Vmp in the range of ~35-38 volts or so (minimum).
With a good quality MPPT charge controller, a person would typically put two Vmp~30 volt panels in series to charge a 24 volt battery bank.
It looks like the Aims may be:
http://www.aimscorp.net/3000-Watt-Pure-Sine-Low-Frequency-Solar-Inverter-Charger-24-Volt.htmlMPPT solar charge controller - PV in 30-55Vdc
If this is true, and the panels are "Grid Tied Style" panels (typically 60 cell / 30 Volt Vmp), two in series would be too high of operating voltage for this controller (sounds like it was designed for Vmp~18 volt or two in series for Vmp~36 volt panels).
All guesses at this point.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Issues with AIMS inverter/charger
Here it is:
* 12) Kyocera 140W 12V panels: http://www.solar-electric.com/kyocera-kd140gx-lfbs-140-watt-polycrystalline-solar-panel.html
* Voc at 10:00am was 20.1V per panel
* He has six parallel strings of two panels in series each. His Voc on each series string is 40.2V (at 10:00am)
* He tested the amperage while it was connected to the charge controller, and said each string was about 5.1A-5.2A. All six strings pegged his ammeter that had a 30A max. He didn't test the Isc.
Dave, That's all I saw on the programming too.
Did that give any insight?
Edit: Just talked to my co-worker, and you're right. He did NOT get the AIMS unit from NAZW&S... he got panels from them. They did tell him it was all hooked up right, though. -
Re: Issues with AIMS inverter/charger
Sounds correct...
Get a volt meter and measure the solar panel input voltage and the output voltage right at the controller/inverter's terminals.
Also, get an inexpensive DC current clamp / DMM like this one from Sears. You can start measuring current and see what is happening.
Also, how many Amp*Hours is the 24 volt battery bank? Any indication of how much solar array/charging current is going into the battery bank when the system is up and charging?
The Voc and current reading sound OK when panels tested individually.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Issues with AIMS inverter/charger
isn't that the brand coot always complained about?
ckhnd,
have you tried contacting aims about it as all else sounds correct? does he have access to another controller to see if bypassing the aims would work? -
Re: Issues with AIMS inverter/charger* He has six parallel strings of two panels in series each. His Voc on each series string is 40.2V (at 10:00am)
* He tested the amperage while it was connected to the charge controller, and said each string was about 5.1A-5.2A.
He has ~1200 watts going somewhere. If nothing is running, it would be unlikely that this could be turned into wasted heat without noticing it. The batteries are known to be good?I am available for custom hardware/firmware development
-
Re: Issues with AIMS inverter/chargerI have read every page in the manual, and there are literally NO adjustable settings for the MPPT charge controller portion, other than a battery type selector (which is set correctly according to the manual).
Does this controller have a remote battery temp sensor?
How does this controller decide how much time to spend in absorb? If you can't make absorb longer, you can try making it a higher voltage by selecting 'calcium' as the battery type. Be sure to watch water levels and battery temperature.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: Issues with AIMS inverter/chargerisn't that the brand coot always complained about?
ckhnd,
have you tried contacting aims about it as all else sounds correct? does he have access to another controller to see if bypassing the aims would work?
Yes.
You may also have noticed I frequently warn against these all-in-one units because of exactly this sort of problem. That is; no flexibility in the design.
My advice is: get rid of it and buy quality equipment that actually works. 1600 Watts of panel should have no trouble charging a single string of L16's as it ought to put out 50 Amps on 24 Volts. The KD140's are true 12 Volt panels so as long as they are configured in strings of two (or four) the Voltage should be high enough (barring serious wiring losses).
And no I do not work for NAWS. -
Re: Issues with AIMS inverter/charger
Let's see:
BB: Batteries are Trojan L16re-a, so 325Ah.
Niel: The AIMS unit has no display other than a few LEDs.
Jonr: The batteries are good, and only three months old. He can run his generator, the batteries will charge and even reach a 'float' state according to the inverter. He has verified the charged state with a volt meter and a hydrometer.
vtmaps: This inverter has no bells or whistles.
Coot: Both my boss and I have Outback MPPT charge controllers. I had a discussion with my co-worker about getting a different charge controller, and he has decided that he will go buy a separate charge controller and bypass the built-in one. At this moment, he wants an Outback, I think because he knows two people that already have them, plus the NAWS guy showed him one and he was impressed with it. I did cringe when we first talked about his equipment and he said, "The MPPT charge controller is built in to the inverter". I also don't believe in putting all your eggs in one basket!
I believe his problem will be solved with a different charge controller.
The rest of the AIMS device seems to work fine, so he probably will just use it for the inverter/ac charger for now. I'm going to recommend to him that he starts saving a little to get a quality inverter down the road. -
Re: Issues with AIMS inverter/charger
Is that a single string of 325 AH batteries on a 24 volt bank? If so, that array is more than large enough to properly charge that battery bank:
12*140 Watt panels = 1,680 Watt array
325 AH * 29 volts charging * 1/0.77 panel+controller losses * 0.10 rate of charge = 1,224 Watt array for 10% rate of charge
5% to 13% rate of charge with 10%+ being a really nice sized array for a daily cycling battery bank.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Issues with AIMS inverter/charger
That's the conclusion we came up with too. -
Re: Issues with AIMS inverter/chargerCariboocoot wrote: »Yes.
You may also have noticed I frequently warn against these all-in-one units because of exactly this sort of problem. That is; no flexibility in the design.
My advice is: get rid of it and buy quality equipment that actually works. 1600 Watts of panel should have no trouble charging a single string of L16's as it ought to put out 50 Amps on 24 Volts. The KD140's are true 12 Volt panels so as long as they are configured in strings of two (or four) the Voltage should be high enough (barring serious wiring losses).
And no I do not work for NAWS.
I and several friends have had nothing but problems with AIMS products. I received a DOA one, then the replacement lasted 2 weeks. I finally forced them to refund my money (Not NAWS; I can't remember where I got it).
Sure, they are cheap, but as you noticed, you get what you pay for. And your time is worth something right? So I agree, dump it NOW otherwise you will be spending more and more of your time messing with it until it finally dies at the worst possible time and leaves you stranded (or ends up killing your battery bank due to undercharging). All-in-one units are like all season tires. They "kinda do the job" but they are not really great in any specific condition.Off-Grid in Central Florida since 2005, Full-Time since June 2014 | 12 X Sovello 205w panels, 9 X ToPoint 220w panels, 36x ToPoint 225w panels (12,525 watts total) | Custom built single-axis ground mounts | Complete FP2 Outback System: 3 x FM80, 2 x VFX3648, X240 Transformer, FLEXnet-DC, Mate-3, Hub-10, FW500 AC/DC | 24 x Trojan L16RE-B Batteries 1110ah @ 48v | Honda EU7000is Generator and a pile of "other" Generators | Home-Made PVC solar hot water collector | Custom data logging software http://www.somewhatcrookedcamp.com/monitormate.html -
Re: Issues with AIMS inverter/charger
Assuming he has loads that are commenserate with the amount of solar panels:
1,680 Watt array * 0.52 system efficiency * 4 hours of sun (typical minimum for non-winter days) = 3,494 Watt*Hours per day
That is a good size system for a very efficient home (refrigerator, lights, well pump, washing machine, laptop, etc.).
If he is using >3kWH per day and/or has shading problems/cloudy skies (marine layer, etc.), then he would have a problem of using more power than the panels generate.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Issues with AIMS inverter/charger
Out of curiosity, I clicked the link and looked at these inverters. First thing I noticed was that the price was half of a comparable Outback, Magnum, etc. If you watch the sales video you would think they are the second coming, military spec, bomb proof, etc. That is why it is good to have real world experienced people's input. I like my old SW4024 but know that someday I will have to change it out so will look at as many options as I can so that I will be ready when the time comes. Outback seems to be the front runner for now. -
Re: Issues with AIMS inverter/charger
Hello all. If I may. It may be the charge is not for solar, but only for the the Ac charging capability. I have been trying to research this inverter in order to make a purchase. I was under the impression the built in charger was non specific, but it would seem that it is not. Bypass built in charger and implement another. This litmus will determine if I buy one. Best of luck. -
Re: Issues with AIMS inverter/charger
Link says it has a 60 amp Solar Charge controller built in plus a 40 amp line charger.GT3.8 w/4600W Trina 230W, TX5000 w/5000W ET-250W, XW4024 w/1500W ET-250W, 4 L16, 5500W Gen. (never had to use) Yet!! -
Re: Issues with AIMS inverter/charger
Hey guys,
I'm also looking at the AIMS units. For the price it's very tempting. I am looking at a Model #: PICOGLF80W48V240VS.
I've heard complaints about rf noise, and premature failure of units , but nothing on this model unit.
I also spoke to a csr online and the few things that stand out is 10% thd , and non functional dc inputs that he said was part of an older design that got carried over.
Any one use these and can shed some light on them? -
Re: Issues with AIMS inverter/charger
Note: 10% THD is so far off grid-quality power as to be unacceptable. It should be 5% or less. Good inverters are around 3%.
This thing sounds like an MSW inverter. -
Last week my 6000 watt low frequency AIMS inverter stopped working. First, the high voltage charger stopped and then later the inverter. I think the solar charger is still working but for the 2 years I have owned it, I have never been satisfied with the solar charger, but it did ok. I have contacted AIMS and they will fix it outside warranty but will have to evaluate the cost once they get it back. Well, I live in Mississippi and they are in NV. $150 freight one way. Now I don' know what to do. If it were just board replacement I could do that and maybe replace the FETS but I'm not getting input from tech at AIMS. This is an all-in-one unit. I would not recommend this for anyone. Component way would be best, especially if some part fails. My unit has an 85 amp battery charger for generator and 60 amp for solar. If I could salvage any part that would help. Has anyone ever worked on one or know of a way to salvage any part of he unit?
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed