wire size
ws9876
Solar Expert Posts: 448 ✭✭✭
what size wire is good for a 70 ft run from the inverter(120v) to the mains box. 2500 watt inverter.
Comments
-
Re: wire sizewhat size wire is good for a 70 ft run from the inverter(120v) to the mains box. 2500 watt inverter.
Well first it has to be able to handle the current, which at maximum power is about 21 Amps. So right away you're at 10 AWG because 12 AWG is rated for 20 Amps continuous (although it would probably work because you'd rarely be at full power).
Second it has to be able to keep the Voltage drop to a minimum over that distance. If you use 10 AWG at 120 VAC and 21 Amps over 70 feet the V-drop is only 2.5% so again that should be fine. If you substitute 12 AWG the V-drop goes up to 4% which is higher than we'd like to see. -
Re: wire size
Remember that a "typical" good quality AC inverter can surge ~2x rated current... So if you have heavy starting loads, you may want to go 3 gauges heavier (3 awg = ~2x cross sectional area = 1/2 the resistance). Of course, in smaller wire gauges, they generally go in 2 AWG steps.
On the other hand, if you have a hard starting load (like a well pump), sometimes the extra resistance helps keep surge currents manageable (higher currents may simply shut down the inverter).
One way around that would be to run two 12 AWG (or 10 AWG) runs from the inverter... Run your lights/computer/radio/etc. on one branch. Run the well pump/skill saw on the second run. That will help you lesson "brown outs" on your more critical loads while keeping high(er) resistance on the high surge circuit.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: wire size
I'd say 6 or 8 ga. Needed to reduce loss if you have surges, and you are likely to want to grow the system in 5 years, and 10ga will have to be replaced.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: wire size
If you trench, drop in several relatively large diameter conduit (I use ABS pipe too)... easy to add/update wiring later.
Lay two--One for AC wiring, the second for communications cabling later.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: wire size
Most important: have the right size circuit protection for the wire.
For example you could use 12 AWG knowing you will never get near the maximum output of the inverter, but it should be on a 20 Amp breaker just in case 'never' happens. That way the breaker trips before the wire fries. -
Re: wire size
would an Outback have 2 outputs for wires out to a mains?? -
Re: wire sizewould an Outback have 2 outputs for wires out to a mains??
I don't understand what you're asking.
Outback inverters have standard 120 VAC wiring for IN and OUT: hot, neutral, and ground. -
Re: wire sizeRemember that a "typical" good quality AC inverter can surge ~2x rated current...
EDIT: In post #7 he asked about an Outback.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed