Questions regarding decoding my codes
93solarcamper
Registered Users Posts: 3
Hello, first thread here. Installed this gear I purchased back in 2012 from Northern AZ Wind and Sun: Kyocera KD140SX-UFBS 140 Watt Solar Module with Junction Box and SunSaver Dual Battery 25 Amp 12 Volt Solar Charge Controller With Digital Meter. Also using 2 6 volt golf cart batteries purchased from Costco and had existing deepcycle 12volt battery already onboard my camper..RV place in Billings Mt installed it all and tied all three batteries together to form 1 12 volt battery. I use a Schumacher 410 watt inverter and just recently experienced low power rating so I topped off my flooded GC batteries with water, they were down slightly, used aprox 1/2 gallon water to fill both 6 volters. System seems to be recovering nicely--currently charging on an overcast day here in southern Orange county Calif on beach. Question I have is how to decipher my remote display information. Anyone out there can give me, a novice layman concerning solar a breakdown on what's what here? One thing that I an confused by is the volts reading : 4.98min, 12.32 max, currently reading 11.76 volts (this reading changes when I turn stuff on). also when I go to the screen that has a little sun in the corner and I can get a current reading of my charging at I assume, 1.67 amps currently) and one reading that has changed it now says 5.03 max and I have another reading in that same field that shows 6518Ah. any help here would be much appreciated.
Jason
Jason
Re: Questions regarding decoding my codes
Welcome to the forum Jason.
First, do you have a DMM (voltmeter) that you can use to start independently measuring voltages? If not, I would highly suggest you get this (or similar) AC/DC current clamp DMM (digital multi-meter) which is "good enough" for our needs.
Next, you need to get a hydrometer and measure/log the temperature corrected specific gravity for each cell in every battery.
From your readings:One thing that I an confused by is the volts reading : 4.98min, 12.32 max, currently reading 11.76 volts (this reading changes when I turn stuff on)
Your batteries have probably been taken DEAD (10.5 volts resting or less, is a dead battery and probably not long for this world even if recharged).
Measuring battery voltage is a tough thing to do and get accurate/interpretable results. Batteries are State of Charge, temperature, and current flow sensitive.
For example, a good battery that has rested for ~3+ hour with no load at room temperature:- ~12.7 volts is full charge
- ~12.0 volts is ~50% charge
- ~10.5 volts is "dead"
When running larger loads (more than 1 amp or so), you probably do not want to see the battery bank operating below ~11.5 volts for very long--That is ~50% state of charge and should be recharged pretty soon (starting in hours or next day).
When charging a battery--You want to see the battery voltage >~12.7 volts minimum. And at least ~13.8 to 14.5 volts when charging well (lots of current, no loads). And you want to see the battery with >14.5 volt held for ~2-6 hours (longer time if the battery is well discharged).
In some cases, you may want to see ~15.0 volts (or more) when equalizing/trying to recover a battery that has been severely discharged/abused.
You don't want to ever expose the battery plates to air--That will ruin the exposed portions very quickly.
So--If your system voltages are correct (11.5 volts when charging)--It is very probably that your batteries are now "toast".
Thanks Bill, one word-Yikes. Currently charging at 11.80 volts, 1.56a . overcast, foggy actually. -
So, you have several steps to take.
Measure the SG of your batteries.
Get the batteries on an AC battery charger (generator/utility power?) and get them >75% charged right now (keep batteries from further sulfating)
Determine if your solar charging system is working (measure charging current/voltage under full sun--A DC Current Clamp Meter is very handy for that).
Fix/upgrade the solar power system (review battery bank size, loads, charging system parameters).
Replace batteries (probably)
Monitor battery bank state of charge with S.G. readings, monitor loads, voltages, charging current--A Battery Monitor (like Tri-Metric) is a very nice to have (but not cheap).
Here is some information about batteries:
http://www.windsun.com/Batteries/Battery_FAQ.htm
http://www.batteryfaq.org/
http://batteryuniversity.com/
=BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
A 140 Watt panel charging with a PWM controller will output ~7.95 amps under full noon time sun with the panel pointing at the sun.
A reasonably sunny mid-day value would probably be from ~4-8 amps charging. Less than that under cloudy conditions, yes, it will be less (can easily be less than ~1 amp on very dark days).
For a pair of 6 volt ~220 AH battery bank, we aim for a 5% to 13% rate of charge (typical rules of thumbs for daily cycling Off Grid loads):- 220 AH * 14.5 volts charging * 1/0.77 panel+controller deratings * 0.05 rate of charge = 207 Watt array minimum
- 220 AH * 14.5 volts charging * 1/0.77 panel+controller deratings * 0.10 rate of charge = 424 Watt array nominal
- 220 AH * 14.5 volts charging * 1/0.77 panel+controller deratings * 0.13 rate of charge = 539 Watt array "cost effective" maximum
A second or third 140 watt panel would be "very nice" if you can swing the costs and mounting space. A single panel is a bit on the small side for a "pure dry camping" system that is used more than weekends/summer.
Anyway--My stake in the ground. Your thoughts, questions, requirements (loads, seasons, etc.).
Things to check include making sure the solar charge controller is close to the battery bank with fairly heavy copper wiring (i.e., 15' of 14 AWG wiring would be legal with one solar panel, but can severely restrict charging current (i.e., battery bank is at 11.8 volts but charge controller is "seeing" 14.5 volts because of excessive voltage drop).
My panel lies flat on the roof of my slidein camper. I occasionally go past 4amps but not for long -
Assuming you are in the southern US, your sun is around 31 degrees this time of year. Flat panels would have a derating of:- 7.95 amps * Cos (90-31 degrees) = 4.1 amps assuming everything else is "ideal"
If you tilted the panel to approximately 60 degrees from horizontal, you would get almost 2x more solar power during the middle of the day. ~45 degrees would be a good compromise for this time of year (assuming you are around 30 Degrees Latitude).
At this point you either assume that everything is working OK and you simply have too much load and/or not enough solar power.
If you wish, we can go through the setup you have right now and figure out if everything is actually working OK. Here is what I would do. First using PV Watts for near where you are at (I pick Los Angeles for now--Move to your true location if different). Fixed array at 0 degree tilt:Month Solar Radiation (kWh/m 2/day) 1 2.88 2 3.87 3 4.77 4 5.76 5 6.57 6 6.79 7 7.00 8 6.60 9 5.13 10 4.15 11 3.21 12 2.72 Year 4.96
Pick ~2.8 of sun at this time of year and I would guess the total amount of AH available per day would average around:- 140 Watts * 0.52 system eff * 2.8 hours of sun = 204 WH of AC power per day (on average)
- 7.95 Amps (full sun) * 0.80 Battery Eff * 2.8 hours of sun per day = 17.8 AH per day (of 12 volt power)
You can also look at the present system design and make sure that everything is OK. Roughly what I would do is get a deceint DMM (or AC/DC Current Clamp DMM) and do some measurements and document your system setup (to review). And give us the results of each step (take voltage/current measurements in the middle of the day with a "discharged" battery bank and/or turn on some battery loads in your RV).- In full sun, measure battery voltage and charging current. If battery is under 12.7 volts, continue below
- Measure the voltage on the Battery Out of the Charge controller
- Measure the voltage on the Solar Panel In of the Charge controller
- Tell us what brand/model of charge controller
- How long and what gauge is the wiring between the charge controller and the battery bank (i.e., 4 feet of 14 AWG cable).
- How long and what gauge is the wiring between the charge controller and the solar panel/array.
For voltage drop between the array and the charge controller, upwards of 0.5 volt is OK, better would be 0.1-0.2 volts.
With a PWM charge controller under full charging current, the Vpanel input will be 0.1 to 2.0 volts higher than Vbatt-charging.
With a MPPT charge controller under full charging current, the Vpanel input will be around Vmp-array (something like 17.5 to 18.6 volts or a bit less).
And, get a decent glass hydrometer and tells us the specific gravity of each cell in the battery bank.
Your choice how far you want to go--But a "small array" and mounted flat to roof is going to put your charging current/total harvest way down during the winter time. During summer, you will get 2+ times more energy harvest and the "flat mounted" panel(s) is less of an issue.
- 234 Forum & Website