Hello Everyone,
I am stumped and i was wondering if someone could help me. I just took ownership of a home equipped with a 1,200W solar array feeding a Xantrex Solar controller that in turn is connected to a Xantrex XW Series Hybrid Inverter/Charger (XW4024-120/240-60). The existing generator was wired to the Xantrex Hybrid Inverter/Charger by means of a 4 wire twist lock plug on the generator side and a (Black(L1),white(N),red(L2),green(G)) wire inside the inverter/charger terminals. The issue is the existing generator is dead as in seized up! The previous home owner purchased a new Honda 2000EU generator, but never hooked it up.
My problem is the Honda 2000EU generator does not have the 4 wire twist lock style outlet, rather it has 2x standard household plugs.
So i "cannibalized" a 50ft medium duty 3 prong extension cord by cutting off one tip and exposing the copper wire so i could wire it to the terminal of the inverter/charger and when i turned it all on, the inverter/charger read-out display indicated AC power was detected but the voltage readout was that of 61v thus the charger does not turn on. Yet i tested the Honda 2000EU and it is in fact outputting 118v at the outlet as well as down the extension cord.
Given that i only have 3 wires to work with and one of them is the "ground" this leaves me with two wires. The diagram of my inverter/charger only shows a line from an illustration that resembles a generator to the gernerator terminal and does not specify which wire goes where.
So if someone here can aid me i would be very grateful.
I've attached two pictures: the first is that of the terminal connections inside the inverter charger and the 2nd is that of the Honda 2000EU panel.
Attachment not found.Attachment not found.
I am stumped and i was wondering if someone could help me. I just took ownership of a home equipped with a 1,200W solar array feeding a Xantrex Solar controller that in turn is connected to a Xantrex XW Series Hybrid Inverter/Charger (XW4024-120/240-60). The existing generator was wired to the Xantrex Hybrid Inverter/Charger by means of a 4 wire twist lock plug on the generator side and a (Black(L1),white(N),red(L2),green(G)) wire inside the inverter/charger terminals. The issue is the existing generator is dead as in seized up! The previous home owner purchased a new Honda 2000EU generator, but never hooked it up.
My problem is the Honda 2000EU generator does not have the 4 wire twist lock style outlet, rather it has 2x standard household plugs.
So i "cannibalized" a 50ft medium duty 3 prong extension cord by cutting off one tip and exposing the copper wire so i could wire it to the terminal of the inverter/charger and when i turned it all on, the inverter/charger read-out display indicated AC power was detected but the voltage readout was that of 61v thus the charger does not turn on. Yet i tested the Honda 2000EU and it is in fact outputting 118v at the outlet as well as down the extension cord.
Given that i only have 3 wires to work with and one of them is the "ground" this leaves me with two wires. The diagram of my inverter/charger only shows a line from an illustration that resembles a generator to the gernerator terminal and does not specify which wire goes where.
So if someone here can aid me i would be very grateful.
I've attached two pictures: the first is that of the terminal connections inside the inverter charger and the 2nd is that of the Honda 2000EU panel.
Attachment not found.Attachment not found.
Comments
-
Re: Generator output not detected on Hybrid charger/inverter PV install
Welcome to the forum.
You've got a problem and it is this: the XW inverter requires a 240 VAC generator and the Honda EU2000i is 120 VAC. It isn't going to work. Somewhere around here there's information about changing the XW to accept 120 VAC in, but basically that generator is rather small for the system anyway.
In other words you should buy a larger, 240 VAC generator. -
Re: Generator output not detected on Hybrid charger/inverter PV install
As I understand, the XW AC inverter is typically wired as a 120/240 VAC unit (split phase north American standard home service wiring).
And, as configured, requires a 120/240 VAC genset--Or the use of a transformer to boost 120 to 240 VAC.
You can re-configure the XW to a 120 VAC only unit (and change the firmware)--Then run a 120 VAC only genset (as I understand).
Your other option is to run a ~20-25 amp @ 24 volt battery charger on your eu2000i... I am not sure, but this Iota DLS-27-25: 24 volt 25 amp regulated battery charger may work on the Honda eu2000i. At ~12 amp input current at 1110 VAC--That is very close to the genset's maximum output rating. There is a 15 amp Iota also available--And your genset would probably last longer if you planned on lots of winter generator run time.
The 15 amp @ 24 volt battery charger and 5% rate of charge would support:- 15 amp * 1/0.05 rate of charge = 300 AH @ 24 volt battery bank
Nominally, I would be suggesting (approximately) an 800 AH @ 24 volt battery bank. And solar panel wise, 5% to 13% rate of charge:- 800 AH * 29 volts charging * 1/0.77 panel+controller derating * 0.10 rate of charge = 3,013 watt "nominal 10% rate of charge" array
Charging wise, 10-20% rate of charge is common for an AC genset:- 800 AH * 29 volts charging * 1/0.90 charger eff * 1/0.75 consumer generator derating * 0.10 rate of charge = 3,437 Watt "minimum-nominal" rated genset
Of course, I am making lots of guesses here--The other 1/2 of battery/solar array/generator charging sizing is the number of Watt*Hours (kWH/Amp*Hours/etc.) of energy you plan/are using today... Your loads define the battery bank. And the battery bank (plus loads) define your charging source needs.
Short/heavy surges (i.e., deep well pump) can also define the minimum battery bank/AC inverter size in some situations. It is all a balancing act here.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Generator output not detected on Hybrid charger/inverter PV install
The XW series, from the factory, require a 240V generator on the AC2 input. You can use a step-up transformer, to boost the genset to 240V and it would barely work. I use a 3Kw generator, which coupled with winter sun, is adequate. There are also settings to allow wider AC input voltage ranges and frequency variations.
You also need to understand the many generator support menu options on the SCP or Combox, and how they react with the battery charge settings, in order to program for the best fuel usage.
What are your winter loads & battery charging expected to be ? Solar harvest ? Do you need a secondary backup generator? (I do, just got a Subaru/Robin diesel 3Kw - w 240V outlet) Do you need Auto Start - that's a whole different range of generators to look at.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: Generator output not detected on Hybrid charger/inverter PV installCariboocoot wrote: »Welcome to the forum.
You've got a problem and it is this: the XW inverter requires a 240 VAC generator and the Honda EU2000i is 120 VAC. It isn't going to work. Somewhere around here there's information about changing the XW to accept 120 VAC in, but basically that generator is rather small for the system anyway.
In other words you should buy a larger, 240 VAC generator.
Thank you for your quick response, i guess i'm off to the hunt to find a 240V Genset!!! -
Re: Generator output not detected on Hybrid charger/inverter PV install
Now i assume my winter needs will be quite close to that of my summer needs given i am located in Panama which is rather close to the equator and i suspect does not fluctuate much but i could be wrong!
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed