charging batteries with my honda 2000 eu
kip martin
Registered Users Posts: 7 ✭
Hola
I have an outback fx and 8 Trojan L- 16 6 volts along with a Honda 2000 eu. We have had several days ( 5 ) without sun as it is raining in the rainforest. ( big surprise ) I may need to charge the batts. with my my gen. I have never done this so I am asking what I need to set my input limits to on my inverter. I have the manual and can find the screens to change the values but can someone give me a starting place for what those values should be?
Thanks Kip
I have an outback fx and 8 Trojan L- 16 6 volts along with a Honda 2000 eu. We have had several days ( 5 ) without sun as it is raining in the rainforest. ( big surprise ) I may need to charge the batts. with my my gen. I have never done this so I am asking what I need to set my input limits to on my inverter. I have the manual and can find the screens to change the values but can someone give me a starting place for what those values should be?
Thanks Kip
Comments
-
Re: charging batteries with my honda 2000 eu
That should say Honda 2000 eu. -
Re: charging batteries with my honda 2000 eu
I set the ACin amps to 12 amps and the Charger Limit Amps to any thing from 6-12 amps depending on how many loads I plan to run on Pass through. You can set them both to 12 amps and let the FX raise and lower the charger amps, but depending on the load, some times it will not react fast enough and the generator will drop out and then re-qualify. So you can play with the Charger Limits and find what suits you.
That will give you about 90% loading max. You should start out with the ECO Off then after it stabilizes you can turn it on. Max charge gives you about 2 hours or so to a gallon and a longer term scheme you can get 5-6 + at lower amps.
I also have another longer term plan I run that says I don't care how long the generator runs and I set the ACin to 6-7 amps and the Charger limit to 4-5 amps and just let the generator idle along. This gives you more power for Pass Through loads that the ECO throttle will pick up and the generator will load and un-load. The GFX also has Generator Support so it plays into this scheme, if I am running a A/C I set the ACin lower and let the Inverter pick up the excess load on the generator and keep it idling and charge more off-cycle.
. -
Re: charging batteries with my honda 2000 eukip martin wrote: »Hola
I have an outback fx and 8 Trojan L- 16 6 volts along with a Honda 2000 eu. We have had several days ( 5 ) without sun as it is raining in the rainforest. ( big surprise ) I may need to charge the batts. with my my gen. I have never done this so I am asking what I need to set my input limits to on my inverter. I have the manual and can find the screens to change the values but can someone give me a starting place for what those values should be?
I presume you have a mate. If not, you can't program your inverter.
In the SETUP menu of the Mate, set the Generator limits to 13 amps. In the ADV (advanced) menu, also set the charging limits to 13 amps.
This means you will run your generator at near its max and it will put all of its power into the batteries. Your batteries can handle the full output of that generator. If you have any AC loads, your inverter will cut back on the battery charging so that the AC loads do not pull more than 13 amps from the generator. (of course, if your AC loads exceed 13 amps, the generator will fault... the inverter can't stop you from overdrawing the generator on a pass-through AC load.
I am able to run my generator with the eco-throttle on... the VFX is fairly gentle when it ramps up its battery charger.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: charging batteries with my honda 2000 euI presume you have a mate. If not, you can't program your inverter.
In the SETUP menu of the Mate, set the Generator limits to 13 amps. In the ADV (advanced) menu, also set the charging limits to 13 amps.
This means you will run your generator at near its max and it will put all of its power into the batteries. Your batteries can handle the full output of that generator. If you have any AC loads, your inverter will cut back on the battery charging so that the AC loads do not pull more than 13 amps from the generator. (of course, if your AC loads exceed 13 amps, the generator will fault... the inverter can't stop you from overdrawing the generator on a pass-through AC load.
I am able to run my generator with the eco-throttle on... the VFX is fairly gentle when it ramps up its battery charger.
--vtMaps -
Re: charging batteries with my honda 2000 eu
Let your pocket book be your guide. I have recorded as high as 5500 rpm as a overspeed before dropout.
Eco on - idle speed 3,000 rpm, maximum speed 5,000 rpm
Eco off- idle speed 4,300 rpm, maximum speed 5,000 rpm
If the electrical load requires an engine speed of 4,300 rpm or greater, the eco switch does nothing. -
Re: charging batteries with my honda 2000 eu
thanks to all responders, very helpful -
Re: charging batteries with my honda 2000 eu
One other thing, at least on My Mate, some may be different. You set the ACin generator Limit from the Main Screen. Select > Setup> FX > Input> choose Grid or Gen ( either works the same, just allows two different settings ) > Set ACin amps> ok .
. -
Re: charging batteries with my honda 2000 eukip martin wrote: »Hola
I have an outback fx and 8 Trojan L- 16 6 volts along with a Honda 2000 eu.
5 days without sun or generator, I expect batteries to be fatally low. 12A charge into a 400ah battery is not going to do much for you. better than nothing, but not much. Let's hope you get some sun soon.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: charging batteries with my honda 2000 eu5 days without sun or generator, I expect batteries to be fatally low. 12A charge into a 400ah battery is not going to do much for you. better than nothing, but not much. Let's hope you get some sun soon.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed