A little help
Gregb
Registered Users Posts: 11 ✭
12 Renogy 100 watt mono panelsl 18.9 VMP 22.5 Voc 5.29 amps IMP 5.75 ISC
outback Flex 80 max input volts 150
24 volt battery bank
I read on another forum,that with a MPPT charge controller the best voltage to run out of my panels is 15v to24 volts above the voltage of my battery bank. Is this correct? if not can I run three strings of 4 panels in series using the 22.5 voc the voltage would be 90 volts. Using VMP of 18.9 =75.6 volts . Next with 1200 watts max from panels am i limited to 1200 watts on my pure sine wave 24 volt inverter Now at best my amps from the panels would be 63.48 amps is there a rule for sizing my 24 volt battery bank so I get the best proformance from this system? As I said I can use a little help.
outback Flex 80 max input volts 150
24 volt battery bank
I read on another forum,that with a MPPT charge controller the best voltage to run out of my panels is 15v to24 volts above the voltage of my battery bank. Is this correct? if not can I run three strings of 4 panels in series using the 22.5 voc the voltage would be 90 volts. Using VMP of 18.9 =75.6 volts . Next with 1200 watts max from panels am i limited to 1200 watts on my pure sine wave 24 volt inverter Now at best my amps from the panels would be 63.48 amps is there a rule for sizing my 24 volt battery bank so I get the best proformance from this system? As I said I can use a little help.
Comments
-
Re: A little help...with a MPPT charge controller the best voltage to run out of my panels is 15v to24 volts above the voltage of my battery bank. Is this correct?if not can I run three strings of 4 panels in series using the 22.5 voc the voltage would be 90 volts.Next with 1200 watts max from panels am i limited to 1200 watts on my pure sine wave 24 volt inverter?Now at best my amps from the panels would be 63.48 amps is there a rule for sizing my 24 volt battery bank so I get the best proformance from this system?Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Re: A little help
Thank you for your help. -
Re: A little help12 Renogy 100 watt mono panelsl 18.9 VMP 22.5 Voc 5.29 amps IMP 5.75 ISC
outback Flex 80 max input volts 150
24 volt battery bank
I read on another forum,that with a MPPT charge controller the best voltage to run out of my panels is 15v to24 volts above the voltage of my battery bank. Is this correct? if not can I run three strings of 4 panels in series using the 22.5 voc the voltage would be 90 volts. Using VMP of 18.9 =75.6 volts . Next with 1200 watts max from panels am i limited to 1200 watts on my pure sine wave 24 volt inverter Now at best my amps from the panels would be 63.48 amps is there a rule for sizing my 24 volt battery bank so I get the best proformance from this system? As I said I can use a little help.
You want (2) 6 panels in parallel string, then connecting the (2) parrallel strings of 6 in series for the best results, for a 24 volt system.
Each string will produce 12V then once you merge those 2 parrallel strings in a series it will multiply by (2) for 24V
ISC is not the power factor for your amps to the MPPT your IMP is which I would assume is 5.54IMP based off of 5.75Isc
6 X 5.54=33.24 amps
(2) strings in parrallel then connected in series would yield 37.8 Vmp
You really only need a Outback Power Flex 60Mppt you don't need the 80Mppt -
Re: A little help
Greg, I hope you saw my faux pas, the strings of 4 - 12 volt nominal panels would likely be the most efficient for charging a 24 volt battery with a MPPT type charge controller, but as I said there might be other reasons for running higher voltage to the controller, like a long wire run.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Re: A little helpGreg, I hope you saw my faux pas, the strings of 4 - 12 volt nominal panels would likely be the most efficient for charging a 24 volt battery with a MPPT type charge controller, but as I said there might be other reasons for running higher voltage to the controller, like a long wire run.
My bad, amps are to high in (2) parallel strings, increasing voltage drop, (3) parallel strings much better.
Either way he only needs a 60MPPT not an 80MPPT. -
Re: A little helpSolarPowered wrote: »You want (2) 6 panels in parallel string, then connecting the (2) parrallel strings of 6 in series for the best results, for a 24 volt system.
Noto bene:
When constructing strings of panels for an array, they go in series not parallel. The strings of panels in series are then connected in parallel.
Do not put them in parallel first and then connect them in series. -
Re: A little helpCariboocoot wrote: »Noto bene:
When constructing strings of panels for an array, they go in series not parallel. The strings of panels in series are then connected in parallel.
Do not put them in parallel first and then connect them in series.
You're right. I didn't think that through.
That would offer 5.45 IMP per string, then in parallel would make 16.35Imp further reducing conductor size and voltage drop. -
Re: A little helpSolarPowered wrote: »You're right. I didn't think that through.
That would offer 5.45 IMP per string, then in parallel would make 16.35Imp further reducing conductor size and voltage drop.
To say nothing of elimination a lot of extra fuses.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed