cant find thread.
rich
Solar Expert Posts: 62 ✭✭✭✭
just the other day I found a thread detailing the best way to hook up differing panels...today and I cant find it anywere to read it...sheeesh..so I will ask the question here(feeling like im being redundant to our resident experts)...After finding this site my whole plan has been re-thought...I have 4 eco-worthy 100 watt panels
VOC...22.41 v
VMP...17.9
IMP...5.59 amp
ISC...6.2 amp
these are poly crystaline
also I have two renergy 100 watt mono crystalline panels
VOC...22.50 v
VMP...18.9 v
IMP...5.29 amp
ISC...5.75 amp
Should I be putting these in two parallel strings in parallel to the controller(12v) and each string containing 1 of the mono panels..I used to think I knew something about this THEN I CAME HERE.LOL...:cool:.If the mods want they can put this in my existing thread as im not sure as to the rules on multiple threads....any input will be bliss...thaNx.
VOC...22.41 v
VMP...17.9
IMP...5.59 amp
ISC...6.2 amp
these are poly crystaline
also I have two renergy 100 watt mono crystalline panels
VOC...22.50 v
VMP...18.9 v
IMP...5.29 amp
ISC...5.75 amp
Should I be putting these in two parallel strings in parallel to the controller(12v) and each string containing 1 of the mono panels..I used to think I knew something about this THEN I CAME HERE.LOL...:cool:.If the mods want they can put this in my existing thread as im not sure as to the rules on multiple threads....any input will be bliss...thaNx.
Comments
-
Re: cant find thread.
We tend towards having questions about your system in your own thread. Makes it less confusing for everyone.
Regarding panels, if you parallel Vmp "matches" within ~10% worse case you are fine.
If you series connect, then match Imp to within 10% of each other.
Some folks like to use 5% or better as the "ideal" match.
For what you have there, I don't see any preference one way or the other.
What brand/model of charge controller do yo have? PWM or MPPT? You want to make sure you do not exceed the voltage or current limits for the controllers (MPPT controllers are "less fussy" about input/output current limits).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: cant find thread.
You've got four of one and two of the other.
As such your choices are all in parallel (PWM or MPPT on 12 Volt system), three strings each made up of any two, or two strings each with two of the first and one of the second (MPPT only).
Both the Vmp and Imp on these panels are so close that they are practically interchangeable.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed