voltage drop calculator confusion
muddome
Registered Users Posts: 9 ✭
I'm confused on what value to enter for my voltage on the NAWS voltage drop calculator.
http://www.windsun.com/Hardware/Voltage_Calc.htm
Do I use my system voltage which is 24v or do I use the Voc from my panels prallel strings which is 133?
Also is the distance one way?
http://www.windsun.com/Hardware/Voltage_Calc.htm
Do I use my system voltage which is 24v or do I use the Voc from my panels prallel strings which is 133?
Also is the distance one way?
Comments
-
Re: voltage drop calculator confusion
The distance appears to be one way (using another calculator with same numbers).
You use the "nominal" or "minimum" operational voltage/maximum current expected at each point in your system.
If is your battery bank--The worst case is ~21 volts for a low battery/high current/high voltage drop (assuming AC input to your inverter).
For the solar array, it can be the Vmp-array-hot, or it can be a volt or two above Vbatt-charging--An MPPT controller would be Vmp-array. For a PWM (less expensive controller), the voltage would be ~Vbatt-charging.
It just depends on how conservative you want to get--Hot copper wire has higher resistance, etc... You will get close enough if you use "nominal" numbers too.
Voltage drop, for example, on a 12 volt battery bank. Assume battery minimum voltage ~11.5 volts and 10.5 volts minimum for inverter operation. The difference is ~1.0 volt drop.
For a 1,200 watt AC inverter, the maximum worst case current would be:
1,200 watts * 1/10.5 volts cutoff * 1/0.85 inverter efficiency = 134.5 amp maximum worst case current @ 1,200 watts
And, most "good quality" AC inverters will power ~2x rated load for a few seconds (starting a pump for example)--So, you the worst case current could be as high as 269 amps... Therefore, you could use 0.5 volts as your maximum "nominal" voltage drop for a 12 volt battery bank (to allow 2x surge current). Or:
0.5 volt/12 volts = ~0.04 = 4% maximum drop
-Bill
PS: To make it clear, Voc (voltage open circuit) would not be your base voltage--Since there is no current flow. You actual voltage drop would be Vmp-array (close enough).Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed