Starting Out: 230W panels and a PWM controller?
WYsolar
Solar Expert Posts: 31 ✭
List....
After many fits and starts I have the opportunity (about 90% sure) that I can begin building my small solar backup project.
I have the opportunity to purchase 2 good used Sharp 230w panels:
Max Power Rating: 230
STC: 230
PTC: 207.4
Vmp: 30.3
Imp: 7.6
Voc: 37
Isc: 8.24
TempCorrI: 0.053
Efficiency: 14.1
Max Fuse Rating: 15
I plan to feed 2x 6v 220Ah sam's club golf cart batteries in a 12v configuration.
I know a MPPT controller would be much better for my project...but they are just too expensive right now. As a result
I was hoping to use a 20A or so PWM controller like the SunSaver 20L.
QUESTION: Would a PWM controller work in such a situation?
It does not have to be the most efficient now...just work well enough to charge my batteries. The batteries are just for emergency backup (I plan on including a Morningstart 300w Ac inverter in the future)...and for running my small Ham Radio. When I save up more $$ I plan on purchasing a small MPPT controller (like the Phocos 100/20 or the new Rogue if the prices stay <$350 or so).
Thanks for the advice.
After many fits and starts I have the opportunity (about 90% sure) that I can begin building my small solar backup project.
I have the opportunity to purchase 2 good used Sharp 230w panels:
Max Power Rating: 230
STC: 230
PTC: 207.4
Vmp: 30.3
Imp: 7.6
Voc: 37
Isc: 8.24
TempCorrI: 0.053
Efficiency: 14.1
Max Fuse Rating: 15
I plan to feed 2x 6v 220Ah sam's club golf cart batteries in a 12v configuration.
I know a MPPT controller would be much better for my project...but they are just too expensive right now. As a result
I was hoping to use a 20A or so PWM controller like the SunSaver 20L.
QUESTION: Would a PWM controller work in such a situation?
It does not have to be the most efficient now...just work well enough to charge my batteries. The batteries are just for emergency backup (I plan on including a Morningstart 300w Ac inverter in the future)...and for running my small Ham Radio. When I save up more $$ I plan on purchasing a small MPPT controller (like the Phocos 100/20 or the new Rogue if the prices stay <$350 or so).
Thanks for the advice.
Comments
-
Re: Starting Out: 230W panels and a PWM controller?
It will work. You'll just be wasting a lot of the power potential from the panels.
Essentially the PWM controller will simply pass the Imp of the panels but @ battery Voltage. So the maximum power will be about Imp * Absorb Voltage or roughly 15.2 * 14.8 = 225 Watts total. As such the charge rate would peak at about 6.8% on those batteries. -
Re: Starting Out: 230W panels and a PWM controller?
Thanks for the reply, Carib.
To clarify...are you saying that the total wattage of my two panels (460) would be derated to 225W total (over a 50% loss) if I use a PWM controller...or that each panel would be derated to 225W (a loss of 3%).
The 3% I could live with...but a loss of 50% would be catastrophic. -
Re: Starting Out: 230W panels and a PWM controller?Thanks for the reply, Carib.
To clarify...are you saying that the total wattage of my two panels (460) would be derated to 225W total (over a 50% loss) if I use a PWM controller...or that each panel would be derated to 225W (a loss of 3%).
The 3% I could live with...but a loss of 50% would be catastrophic.
That would be the total Wattage: two panels at Imp 7.6 each = 15.2 Amps current. The Voltage is then fixed by the system. With 14.8 Volts on Absorb .... 15.2 * 14.8 = 225 Watts total.
The massive loss comes from the panels' Voltage potential of 30.3 not being utilized by the PWM controller. It can't be helped. Sorry. -
Re: Starting Out: 230W panels and a PWM controller?
the economics of the situation suddenly becomes clear, you are paying more for the MPPT controller to 'access' that > 50% 'lost' power. Pretty cheap power? $233 vs $78 Just no way get to that power when you have GT panels
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Re: Starting Out: 230W panels and a PWM controller?Thanks for the reply, Carib.
To clarify...are you saying that the total wattage of my two panels (460) would be derated to 225W total (over a 50% loss) if I use a PWM controller...or that each panel would be derated to 225W (a loss of 3%).
The 3% I could live with...but a loss of 50% would be catastrophic.
It's not as bad as all that, you can expect to get the 225 watts. The expected output from the 2 - 230 watt panels is likely 80-85% of their panel rating, This is called the NOCT value (Normal Operating Cell Temperature) as panel heat up their voltage is reduced, since you have plenty of voltage you won't have these losses.
I went and hunted down the spec sheet on What I suspect your panels are;
http://www.pvpower.com/pdf/datasheets/sharp/pv%20modules/sharp%20230.pdf
Your panels 230 watts at 25 degrees C operating temp, but looses .485% of it's voltage for every degree above 25, and the NOCT temp of 47.5 so you loss about 11% of your voltage...
Remember to that the charge controller typically, starts reducing the output as your batteries reach 85% of capacity, as we recommend you don't discharge below 80% on a regular basis, it will be at it's worse when you have significantly discharged your battery.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Re: Starting Out: 230W panels and a PWM controller?
Wow.
Sure enough. Pricewise you just can't win.
BTW...what are "GT panels"? -
Re: Starting Out: 230W panels and a PWM controller?
abbreviation for grid tie. -
Re: Starting Out: 230W panels and a PWM controller?
GT panels = grid tie as Niel said, meaning ones whose Vmp is not ideally suited for battery-based systems using a PWM controller. -
Re: Starting Out: 230W panels and a PWM controller?
Thanks again for the kind advice.
It seems to be a catch-22 situation.
12v panels = higher cost for given wattage, but can use lower cost controllers
"GT" panels = lower cost for given wattage, but require much more expensive MPPT controllers to harvest the same energy.
Hard to justify a $400+ controller for my little solar 220Ah battery project. Hmmm. -
Re: Starting Out: 230W panels and a PWM controller?
Here's a sample calculation that I did when considering 12V panels v GT panels...
Four 210W @ $150 each=$600 + $500 60 Amp MPPT = $1,100 for 840 Watts and 54 Amps peak current on a 12 volt system
Or
Four 135W @ $300 each =$1,200 + 45 Amp TriStar PWM @ $150 = $1,350 for 540 W and maybe 30 Amps peak current on a 12 Volt system
For prices, I used the going rate here in Ottawa.
I ended up going with Option 1 and managed to pick up a Classic 150 for less than $500 at the Midnite Garage Sale. (I also decided to go with a 24V system) -
Re: Starting Out: 230W panels and a PWM controller?12v panels = higher cost for given wattage, but can use lower cost controllers
"GT" panels = lower cost for given wattage, but require much more expensive MPPT controllers to harvest the same energy.
Actually, you will harvest more of your panel's potential with the MPPT controller.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: Starting Out: 230W panels and a PWM controller?
As a newbie, may I assume (uh oh) that if MY panels are rated at only 18v (100W, 5.7A) that I would not have this massive loss using the same PWM controller? -
Re: Starting Out: 230W panels and a PWM controller?KnowledgeSponge wrote: »As a newbie, may I assume (uh oh) that if MY panels are rated at only 18v (100W, 5.7A) that I would not have this massive loss using the same PWM controller?
You are correct. The current stays the same, the Voltage changes:
5.7 Amps @ 14.8 Volts Absorb on a 12 Volt system = 84 Watts, only 16% less than the rating.
The "extra" Voltage of the panel is needed to overcome wiring and heat losses. -
Re: Starting Out: 230W panels and a PWM controller?Cariboocoot wrote: »You are correct. The current stays the same, the Voltage changes:
5.7 Amps @ 14.8 Volts Absorb on a 12 Volt system = 84 Watts, only 16% less than the rating.
The "extra" Voltage of the panel is needed to overcome wiring and heat losses.
Cool, thx :cool:
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed