Mix and match panels on a SB 2000e
westbranch
Solar Expert Posts: 5,183 ✭✭✭✭
I read a thread over on the Outback site about Crewzer's solar menagerie. My question is about the advisability/performance of putting together the following:
the SB 2000 has a 20 amp input rating / max 25 amps.
I have 2 Mitsub 120 w panels Isc 7.75 A, Imp 6.69 A total Imp = 13.38 A, Voc 22.0, Vmp 17.6
I want to add another panel to get closer to the 3%-of-capacity target for charging.
3 panels will give me 20.46 A Imp. Over the 20 amp design spec. so no go...
My local shop has a 110 w Mitsub panel Isc 7.16, Imp 6.43 A, Voc 21.2, Vmp 17.1.
Using the 110 w panel would get me just under 20 amps (19.81) but what would the effect of the mix/match be? would I still get the 19.81 A I am after?
TIA
Eric
the SB 2000 has a 20 amp input rating / max 25 amps.
I have 2 Mitsub 120 w panels Isc 7.75 A, Imp 6.69 A total Imp = 13.38 A, Voc 22.0, Vmp 17.6
I want to add another panel to get closer to the 3%-of-capacity target for charging.
3 panels will give me 20.46 A Imp. Over the 20 amp design spec. so no go...
My local shop has a 110 w Mitsub panel Isc 7.16, Imp 6.43 A, Voc 21.2, Vmp 17.1.
Using the 110 w panel would get me just under 20 amps (19.81) but what would the effect of the mix/match be? would I still get the 19.81 A I am after?
TIA
Eric
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada
Comments
-
Re: Mix and match panels on a SB 2000ewestbranch wrote: »Using the 110 w panel would get me just under 20 amps (19.81) but what would the effect of the mix/match be? would I still get the 19.81 A I am after?
Maybe. So we are on the ragged edge. Do you currently see the full power from your panels, or are you shy the normal 15% ? Any idea what cloud edge effect has on your system - will it exceed the 25A ? (only lasts a few seconds, not minutes)Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: Mix and match panels on a SB 2000e
Mike, not sure about reaching max panel output, only there on weekends and in the summer, if it will happen it is now, spring time, cool clear skies. No batt monitor as yet, XBM on order.
No idea as to edge effect, we get lots of potential as in the mountains.
Eric
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Re: Mix and match panels on a SB 2000e
Eric,
This post may set off a howl of protests. I urge you to read the post in its entirety before drawing any conclusions or making any decisions.
My interpretation of the NEC is that the SB2000E’s input current limit is 20 A Isc STC, and not 20 A Imp STC. This issue doesn’t seem to be addressed particularly well in the 2000E’s manual, but it is fairly well covered in the manual for the similar 2512 controller.
Since the total Isc of your two present modules in parallel is 15.5 A, you’ve only got 4.5 A of Isc NEC-compliant-current-headroom remaining. That translates into a "12 V" module rated at ~70 W STC or so.
One issue is whether you want to follow the NEC requirements or not. Since the SB2000E’s output current limit is 25 A, you also need to consider the cold-weather MPPT effect on array voltage to the controller and charge current from the controller. Or, you can design for a 95% “safe” solution and hope that the controller’s thermal management and output current limiting features do their jobs.
In that case, you could hook up an array rated at (14.4 V x 25 A) / 90% = 400 W STC and hope for the best. My gut feel is that the 350 W array you’re considering would probably work just fine >99% of the time, but I don’t know enough about your array’s environment.
Another possibility might be to place a switch in series with the 110 W module and disconnect that module from the array when ambient temps are low, PV array voltage is high, battery voltage is low, and charge current is high.
HTH,
Jim / crewzer -
Re: Mix and match panels on a SB 2000e
Eric,
I would contact Blue Sky Tech support and ask them about the input/output current and if the unit has internal current limits or not...
Personally, I am of the opinion that a well designed MPPT controller can easily withstand being connected to panels that output upwards of 25% (or more--depending on wiring and equipment connected) without any issue at all.
A MPPT controller should have internal limits on power conversion and output current--just like virtually every computer switch mode power supply made in the world today does.
You are looking at STC rated panels, and I find (in the SF Bay Area which does not get very cold) that my Grid Tie system rarely (maybe once or twice a year) gets close to the PTC ratings (~85% or so of the STC rating) of the system...
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Mix and match panels on a SB 2000e
Thanks Jim and Bill, I do have an inquiry off to BlueSky on the units limits, still waiting for a reply.
I expect (hope) their answer will clarify the Isc vs Imp issue.
Eric
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Re: Mix and match panels on a SB 2000e
Jim, Bill, I found the reference to 20 A Isc MAX .
It is buried in the fine print in installation instructions... rather than specs...
So that puts an end to that plan, taking into account edge effects, safety margins, etc.
Hope the Classic get released soon... or an MX60 will be needed... jump in with both feet eh?
thanks again for the help.
Eric
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Re: Mix and match panels on a SB 2000e
to add a footnote here, out of curiousity, i looked at my sb50 specs and it also mentions isc and not imp. now that's an interesting way of upping the appearance of one's specs to be slightly better than they are.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed