#6 wire to panels
Court
Registered Users Posts: 5 ✭
I have 2 145 watt panels and a Blue Sky 2512iX controller on my boat. The panels are 18 V. Round trip from the batteries (440 Ah) is about 45 feet.
The controller cannot accept more than 28 V, so the panels have to be wired in parallel. To minimize loss, I will use #6 wire (tinned marine cable).
What is the proper way to connect the #6 wire to the MC4 connectors? Is there a MC4 connector that will fit #6 wire? If I can't find an MC4 connector, I will crimp eyes on each cable, bolt them together and pot the connection. The problem with potted connections is that I will have to destroy them every time I have to take the panels down for hurricane warnings.
The controller cannot accept more than 28 V, so the panels have to be wired in parallel. To minimize loss, I will use #6 wire (tinned marine cable).
What is the proper way to connect the #6 wire to the MC4 connectors? Is there a MC4 connector that will fit #6 wire? If I can't find an MC4 connector, I will crimp eyes on each cable, bolt them together and pot the connection. The problem with potted connections is that I will have to destroy them every time I have to take the panels down for hurricane warnings.
Comments
-
Re: #6 wire to panels
Might put a combining box at the panels, or since you just have 2 panels use a distribution block to combine them. I think #8 is the largest of the mc4 connectors and most only go to #10.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Re: #6 wire to panelsI have 2 145 watt panels and a Blue Sky 2512iX controller on my boat. The panels are 18 V. Round trip from the batteries (440 Ah) is about 45 feet.
The controller cannot accept more than 28 V, so the panels have to be wired in parallel. To minimize loss, I will use #6 wire (tinned marine cable).
What is the proper way to connect the #6 wire to the MC4 connectors? Is there a MC4 connector that will fit #6 wire? If I can't find an MC4 connector, I will crimp eyes on each cable, bolt them together and pot the connection. The problem with potted connections is that I will have to destroy them every time I have to take the panels down for hurricane warnings.
Why is it that you need #6 conductors? That seems like extreme overkill to me. At 30 degrees C, #6 conductors with 90 degree insulation in free air are rated at 105A. -
Re: #6 wire to panels
Court, Welcome to the forum.
Do NOT cut, pot, or damage the MC4 connectors on your panels. Buy a cable with MC4 connectors on each end and cut it in half. Use the MC4 end to connect to your panels and the cut end to connect to your combiner box.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: #6 wire to panels
I need #6 to minimize the voltage drop. #8 is okay for a 25 Amp electric battery charger, but off grid, I want to be able to use everything I can collect. -
Re: #6 wire to panels
Where can I buy #6 cables with MC4 connectors? -
Re: #6 wire to panelsWhy is it that you need #6 conductors? That seems like extreme overkill to me. At 30 degrees C, #6 conductors with 90 degree insulation in free air are rated at 105A.
Voltage drop problems I'd say; trying to keep the amount under 3%. 23 feet round-trip on a 12 Volt system carrying 16 Amps and you get 6 AWG wire. Those numbers may not be entirely accurate of course. -
Re: #6 wire to panelsWhere can I buy #6 cables with MC4 connectors?4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i
-
Re: #6 wire to panels
Usually, the easiest is to purchase a short Male/Female MC4 pre-made cable. Cut in 1/2 and connect the cut ends to your 6 AWG wire runs.
8 Foot MC4 Extender Cable Male/Female
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: #6 wire to panels
This points out the problem with many of the older technology analog MPPT conrollers, such as the Blue Sky. Nearly all newer design MPPT controllers can take much higher input voltages. They do tend to cost a little more, but as this problem shows, any cost savings can be eaten up with extra wire costs.
Unfortunately, most people find this out only after they have purchased their charge controller. -
Re: #6 wire to panels
There are some wire type branch connectors out there, that have 6" of wire or so coming into a 'Y', where you can combine your 2 panels mc4 connectors, then you'd just have to worry about 2 butt end connections, clip the continuing mc4 connector off the branch and butt in your #6, still no fun in a marine situation.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Re: #6 wire to panelsUsually, the easiest is to purchase a short Male/Female MC4 pre-made cable. Cut in 1/2 and connect the cut ends to your 6 AWG wire runs.
Another question answered...) Thanks, Photo...Off Grid System; 2175W array; 370ah @ 48v (8 L16 Scrubbers in series); XW MPPT60-150 CC; OutBack VFX3648, FlexNet and Mate
-
Re: #6 wire to panels
Actually Bill should be creditted with that...
Attachment not found.
This is the wire type branch connector I was speaking of, hot linked from outside site, hope that's cool.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Re: #6 wire to panels
Ooops..Sorry there, Bill..Off Grid System; 2175W array; 370ah @ 48v (8 L16 Scrubbers in series); XW MPPT60-150 CC; OutBack VFX3648, FlexNet and Mate
-
Re: #6 wire to panels
The wire Y connector would be perfect, even found them online for $14. Unfortunately, I already ordered branch connectors and a short cable to cut and splice, the $80 solution.
Thanks for all of the suggestions. I'll be back, because I'll probably want to increase the charging voltage to my Trojan batteries, I think that is an expensive thing to do with a Blue Sky 2512iX. I should have done more research!!! -
Re: #6 wire to panels
Our host does sell a version of the Y cables too...
Multibranch MC4 Connectors, Latching
Problem is that they (from how I would use them) are limited to parallel connections of a maximum of two parallel strings... Over that, one should use a combiner box of some sort (with fuses/breakers) for proper electrical safety of the solar array.
Note too--the new forum software stores/serves images locally by default--So those were not "hot linked". However, I do believe in credit, so feel free to place a link to the original site if you wish.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: #6 wire to panels
The local host version of the Y is what I ordered. The wire Y would have eliminated a connector and the need to purchase an extra cable to split.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed