power shed grounding, etc
jtdiesel65
Solar Expert Posts: 242 ✭✭✭
I'm moving (and upgrading) my current system into an outbuilding. My current scenario is one ground bar outside my house that is tied to DC disconnect, SW inverter box, and main AC panel. Bat neg and AC neg are bonded to ground. The outbuilding scenario is basically the same component setup including a main AC panel. I'm running a line from the outbuilding AC panel to the AC panel in the house. This includes a ground wire, but it's shielded. (Although I have to wonder if that's even necessary since neg is bonded to ground in the outbuilding) I would think I need a ground rod for the outbuilding that duplicates what I have in the house. But should I keep the house AC panel to ground rod tie?
I'm wondering if having a ground rod at the outbuilding and a ground rod at the house is cause for a ground loop.
Also, for GFP on charge controllers. From what I read GFP won't work with my current setup due to bat neg/ground bond. I was planning to change from outback charge controllers to Classic charge controllers. I think GFP can be disabled, but is there any change I should make to keep GFP?
I'm wondering if having a ground rod at the outbuilding and a ground rod at the house is cause for a ground loop.
Also, for GFP on charge controllers. From what I read GFP won't work with my current setup due to bat neg/ground bond. I was planning to change from outback charge controllers to Classic charge controllers. I think GFP can be disabled, but is there any change I should make to keep GFP?
Comments
-
Re: power shed grounding, etc
If you're going to use Midnite's GFDI you need to read through this: http://www.midnitesolar.com/pdfs/DC%20Ground%20Fault%20Protectors%20explained.pdf
Note the bit at the end: "You do not ground the battery negative when using the DC-GFP since the DC-GFP is now the
battery negative to earth ground bond."
Yes; wiring changes are required.
As for the other grounding issues, it's best to have one AC neutral to ground bond and one Earth ground rod. Other configurations have the potential to form ground loops. That said, it is sometimes necessary or preferable to have a separate ground rod elsewhere if the distance between them is great enough (soil resistance between the two points reducing the ground loop potential).
Stand by for further and no doubt conflicting opinions on this; proper grounding is one of the most argued-about aspects of electrical theory.
Personally I would not use the DC GFDI as I remain unconvinced as to its efficacy. I'm not keen on AC GFCI either, except in certain applications. -
Re: power shed grounding, etcjtdiesel65 wrote:I would think I need a ground rod for the outbuilding that duplicates what I have in the house. But should I keep the house AC panel to ground rod tie? I'm wondering if having a ground rod at the outbuilding and a ground rod at the house is cause for a ground loop.
As for the house, you may or may not need a ground rod and bonding. The best way for you to research this is to figure out the rules in your jurisdiction for subpanels. This comes up a lot with garages. If the power enters an attached garage, the house panel may be a subpanel (unbonded) of the main garage panel. If the power enters a detached garage, well, I never did figure out what is the right thing to do. It may be a gray area of the code. Inquire of your building inspector.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: power shed grounding, etc
Whats' the distance from house, to outbuilding ?Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: power shed grounding, etc
Thanks Its 100ft. From the house it goes to a detached garage to another panel. -
Re: power shed grounding, etc
for 100', they want me to use a separate ground after 50', so I think you are going to have to do that too, at the house service entry.
I'm 300' from the battery shed, and 120' from the sub panel at the pump house. 3 ground rods, and a creek & 20' deep ravine in between.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: power shed grounding, etc
Agreed. With 100' distance between them, I see no problem with a second Earth grounding rod at the shed.
Although you may need to unbond the neutral in the house if it is bonded in the shed; the neutral & ground wires running between locations could cause a potential loop on them.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed