Thread: Charging a Sealed Lead Acid Battery

  1. #1

    Default Charging a Sealed Lead Acid Battery

    Hi all,
    I'm trying to calculate the time to recharge a sealed lead acid battery to 100%. For example if I have a battery at 100%, and I discharge 10A for 1 hour, will it take exactly 1 hour to recharge the battery if my charger supplies 10A of charging current? Or will it take 1.1 hours, 1.2 hours, etc. Is there a term for that? ("charging efficiency?") I've looked on battery datasheets and I can't seem to find anything to answer my question.
    Thanks for any help.

  2. #2

    Default Re: Charging a Sealed Lead Acid Battery

    Pretty much, and my experience is from Flooded batteries, there is no correct answer. As batteries approach full capacity they can accept less current. You do get close to 1:1 - 1:1.1 correspondence in the 50%-85% with the charging voltage appropriate.
    Home system- 20 - 200W Evergreen blems, 2 Classic Lites, E-Panel, Prosine 1800 watt inverter, up and running 1 Classic Lite and 14 Suntech 185W in spare room.
    Cabin system- 8-115watt 12V, 6 - 170-5watt 24v, Pulse/Trace PC250 Power Center, 800AH 24V forklift Batt, ProSine 1800 watt (24v) inverter.
    Odds and extras, Rouge CC, 80-4/5watt 6v panels

  3. #3

    Default Re: Charging a Sealed Lead Acid Battery

    Quote Originally Posted by diego96 View Post
    I'm trying to calculate the time to recharge a sealed lead acid battery to 100%. For example if I have a battery at 100%, and I discharge 10A for 1 hour, will it take exactly 1 hour to recharge the battery if my charger supplies 10A of charging current? Or will it take 1.1 hours, 1.2 hours, etc. Is there a term for that? ("charging efficiency?") I've looked on battery datasheets and I can't seem to find anything to answer my question.
    It is up to you how much you put back. With flooded batteries, the more you put back, the more bubbling you get. So, by varying the amps you can vary the amound of energy that goes to bubbling and efficiency changes accordingly. The correct amount of bubbling is important to flooded batteries. Sealed batteries do not need bubbling, so you should get something close to 1 or slightly higher.

    The energy efficiency is worse than amp-hour efficiency because you charge at higher voltages and discharge at lower voltages.
    Off-grid: 6.12kW SolarWorld, 8 Trojan IND13-6V, XW6048, 2 XW MPPT60-150, 10kW Generac, 5kW Champion

  4. #4
    Join Date
    Jun 2007
    Location
    Williams Lake, BC
    Posts
    2,819

    Default Re: Charging a Sealed Lead Acid Battery

    What does the maker recommend for charge parameters? Since they are sealed you should not EQ for one thing and, secondly the charge rate should be lower than FLA to avoid too much gassing... the H and O2 have to recombine into H2O.
    100% Off Grid @ 51* 46' N lat 124* 44' W long

    New House system: coming - 2 arrays @ 2240W
    CL150&Epanel 2 @140 W 12v PVs , 24V C&D AT-15P AGM @ 950Ah
    + CL150 2@120W 12 V panels, 24V C&D AT-15P AGM @ 950Ah
    Cotek ST1500W inverter, TBS 30a-24v Omni-charger, Honda Eu3000is,

    Guest cabin system: 3 - 70W panels to SB 2000e CC, with 2 - 100 ah 12v SAFT wet NiCd's , 600W TSW Inverter

  5. #5

    Default Re: Charging a Sealed Lead Acid Battery

    Quote Originally Posted by westbranch View Post
    What does the maker recommend for charge parameters?
    Powersonic sealed lead acid battery. Constant current (max 22A) up to 14.4V, hold at constant voltage 14.4V until current drops below 750mA. Battery is 100% at this point.

  6. #6

    Default Re: Charging a Sealed Lead Acid Battery

    I don’t know if this is a universal formula but this is what the manual for Sun Xtender batteries says. The Sun Xtenders are AGM batteries. I believe that AGM batteries are considered to be “sealed lead acid”.

    Time to Reach Full Charge = [(DOD/100) X Rated Capacity (Ah) / Rated Output of Charger (Amp)] + 2 hours
    For example, charging a 100ah battery at 50% DOD using a 25A charger would take:
    Time to Reach Full Charge = [(50/100) X 100Ah/25A] +2 hours = 4 hours
    Note that this formula is approximate and the full charge state should be verified using the criteria: current drops below 0.5% of the rated capacity (0.5A for a 100Ah battery).
    6 - Trina 235 Watt panels, TriStar MPPT60 CC, 8-AGM 305AH 6V batts, Magnum MS4024PAE inverter, ME-BMK battery Monitor, ME-ARC Remote Control, MidNite Solar MNDC250, 10KW Generator

  7. #7
    Join Date
    Mar 2006
    Location
    SF Bay Area (California)
    Posts
    19,653

    Default Re: Charging a Sealed Lead Acid Battery

    That is what I use... But I would suggest that the time would be 2-4 hour range... The deep cycled the battery, the longer the "tail" of the charging cycle.

    Also, Concorde batteries are AGM sealed lead acid--But they claim to be "different" from other AGM batteries and are able to accept higher charging voltages (and currents) that other brands may not.

    -Bill
    20x BP 4175B panels (replacement) + Xantrex GT 3.3 inverter for 3kW Grid Tied system + Honda eu2000i Inverter/Generator for emergency backup.

  8. #8

    Default Re: Charging a Sealed Lead Acid Battery

    Another charger question.
    This is what my battery datasheet says: "Limit initial charging current to 22A."
    I'm looking at using a Xantrex TRUECharge2 40A charger. The reason for getting a 40A charger is because I want to sometimes power a load in addition to charging batteries.
    However if there is no load, will the charger try to force 40A into the battery? I assume that would damage the battery since the datasheet says limit to 22A...

  9. #9
    Join Date
    Sep 2006
    Location
    Willits, CA
    Posts
    5,407

    Default Re: Charging a Sealed Lead Acid Battery

    Quote Originally Posted by diego96 View Post
    Another charger question.
    This is what my battery datasheet says: "Limit initial charging current to 22A."
    I'm looking at using a Xantrex TRUECharge2 40A charger. The reason for getting a 40A charger is because I want to sometimes power a load in addition to charging batteries.
    However if there is no load, will the charger try to force 40A into the battery? I assume that would damage the battery since the datasheet says limit to 22A...
    Yep. Maybe. If the battery was totally dead, it could pull the full 40A. But since you will have some charge in it, it will draw less, and as it approaches full, even less. That's why it takes such a long time to complete the last 20% of charge.
    http://tinyurl.com/LMR-Solar
    http://tinyurl.com/LMR-BigLug
    http://tinyurl.com/LMR-NiFe

    Grundfos 10 SO5-9 with 3 wire Franklin motor (1/2hp 240V 1ph # 214505 ) on a timer for 3 hr noontime run - Runs off PV
    Powerfab poletop PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe battery | 15, Evergreen 205w "12V" PV | Midnight ePanel || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT

  10. #10
    Join Date
    Jun 2007
    Location
    Williams Lake, BC
    Posts
    2,819

    Default Re: Charging a Sealed Lead Acid Battery

    As mike said, if the battery is deeply discharged the TC40 will attempt to put 40 amps into the battery. The acceptance rate is dependent on the battery SoC... If yours (TC40) is the same as mine, the display will show the Amps being delivered...
    100% Off Grid @ 51* 46' N lat 124* 44' W long

    New House system: coming - 2 arrays @ 2240W
    CL150&Epanel 2 @140 W 12v PVs , 24V C&D AT-15P AGM @ 950Ah
    + CL150 2@120W 12 V panels, 24V C&D AT-15P AGM @ 950Ah
    Cotek ST1500W inverter, TBS 30a-24v Omni-charger, Honda Eu3000is,

    Guest cabin system: 3 - 70W panels to SB 2000e CC, with 2 - 100 ah 12v SAFT wet NiCd's , 600W TSW Inverter

Similar Threads

  1. exploded flooded lead acid battery
    By jimbob01 in forum Off Grid Solar & Battery Systems
    Replies: 11
    Last Post: November 19th, 2013, 11:15 PST
  2. Charging voltages lead acid deep cycle vs starting
    By landyacht.318 in forum General Solar Power Topics
    Replies: 16
    Last Post: July 2nd, 2013, 11:22 PDT
  3. Typical Sealed flooded lead acid internal rsistance ??
    By SirSparks in forum Solar Beginners Corner
    Replies: 14
    Last Post: September 15th, 2011, 18:21 PDT
  4. Wet/Lead Acid "Maintenance Free" car battery Charging
    By Wanderman in forum Solar Beginners Corner
    Replies: 6
    Last Post: June 24th, 2011, 8:40 PDT
  5. Lead Acid battery SOC sensor
    By RCinFLA in forum Advanced Solar Electric Technical Forum
    Replies: 0
    Last Post: August 25th, 2010, 20:11 PDT

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •