Hola Amigos,
We've been installing U.S. Battery L-16HCs for a number of our clients. We followed their charging recommendations which are here:
http://www.usbattery.com/usb_faqs.html
Using their specs, the recommended charging voltage works out to 61.992 volts in a 48 volt system. This seems awfully high compared to other battery charging recommendations, and I've grown increasingly worried we're frying these batteries at this level. We have a couple of installs that are using a lot of water after a few years.
We're using Outback MX-60 charge controllers with default charge/absorb settings, only changing the bulk charge and float voltages. Typical installation is 8 L16s with between 1,350 to 1,800 watts in panels. Temperatures during the summer can reach 95 for a couple of months.
    Re: US Battery Charging Specs
    AlanRT wrote: »
    Odd, because if you were cooking the batteries, they would be using water the first month.
    I wonder if the owners are ignoring them till they get a problem (low water).
  • dwh
    Hi Alan,
    You never did let us know what happened with that generator install. I, for one, would love to hear how it turned out.
  • AlanRT
    I'll answer in that thread (if I can find it)
  • AlanRT
    Anyone have any more input about these charging specs for US Battery?
  • rplarry
    rplarry Solar Expert Posts: 203 ✭✭
    I agree 61.9v seems awfully high compared to Trojans 59.2v, but how are you going to argue with the manufacturer? FLAs are very forgiving, as long as there is liquid covering the plates they can handle almost anything you can give them. Maybe US Battery has a sulfation problem and they are trying to keep that at bay by using a higher voltage. ?Quien sabe?
    Larry
  • AlanRT
    I put the question to US Battery this morning.
    I'll post the response once I get it.
    Saludos
    61V sounds like the EQ cycle voltage, not the daily absorb / float voltage.
  • AlanRT
    I know, but that's what they're saying in their FAQs.
    Probably an issue between "fast charge" capabilities vs floating (longer term/non-use/storage).
    Too much "equalization" creates oxygen around the positive plates and will cause corrosion/failure in the positive plates (other pictures here of VRLA batteries with positive terminals / battery tops being pushed up because of corrosion).
    If the >60 volts charging has an appropriate termination setup (typically charging current falling by something like 90%) and then dropping back to float voltage--then all should be OK.
  • crewzer
    Alan,
    I'm generally a stickler for mfr instructions, but I've never been comfortable with US Battery's instructions.
    Instead, and as Bill has suggested above, I like the "High Voltage / Short Time" strategy for winter battery charging (relatively "short" days), and "Low Voltage / Long Time" strategy for summer charging.
    You may find this old Rolls / Surrette Bulletin #614 to be useful.
    HTH, and good luck!
    Jim / crewzer
  • RCinFLA
    RCinFLA Solar Expert Posts: 1,484 ✭✭✭✭
    That high a bulk setting is especially strange with their recommend C/10 rate for stage one which is pretty conservative. At that relatively low phase 1 rate the battery is going to be pretty fully charged when it get to bulk voltage.
    I would not subject batteries to that bulk level on every recharge. A lead acid battery is a lead acid battery. Theirs are not especially different.
    A friend of mine has US battery golf cart size and they all died from plate oxidation in about two and half years. (high cell resistance)
  • AlanRT
    Interesting Reply From US Battery...
    [FONT=&quot]K. Fred Wehmeyer[/FONT]
    [FONT=&quot]Vice President - Product & Process Engineering[/FONT]
    [FONT=&quot]U. S. Battery Manufacturing Company[/FONT]
    [FONT=&quot]1895 Tobacco Road[/FONT]
    [FONT=&quot]Augusta, GA 30906[/FONT]
    [FONT=&quot]Ph: 706-790-0218
    [/FONT]
    [FONT=&quot]The 2.583 volts per cell ([/FONT][FONT=&quot]61.992 volts in a 48 volt system) should only be used with time limited charge profiles and charge voltage that is temperature compensated.[/FONT] [FONT=&quot] [/FONT]
    [FONT=&quot]Note: The equalization mode in the MX-60 is not temperature compensated. Without temperature compensation, equalization charge voltage should be limited to <2.50 vpc (<60.0 volts for a 48 volt system).[/FONT]
    [FONT=&quot]Following are recommended charge settings for single stage, 2-stage, & 3-stage charging systems. Even though the Outback MX-60 claims to be a 3-stage charge controller, it is actually a 2-stage [/FONT]
    [FONT=&quot](bulk and absorption without a finish charge stage). Float and equalization stages are not considered as charge stages since they are charge maintenance stages.[/FONT]