Parallel battery bank wiring diagram
Perfect? Pretty much not going to happen.
But assuming they are the same age, make and model, the idea to have the same resistance across each string. In this case a since you have so many strings, You should incorporate a busbar for each the positive and negative battery cables;
Use the same length and gauge cables to connect each battery.
I've not personally tried this, but... http://www.iotaengineering.com/pplib/balancedcharging.pdf
Photowhit said:Perfect? Pretty much not going to happen.
The (+) main power cable connects to "top end" (near battery #1) of (+) copper bar
The (-) main power cable connects to "bottom end" (near battery #8) of (-) copper bar. -
There is no "opposite diagonal" connection with a buss bar. Every battery gets it's own cables.
Tthe how's and why's of connecting 4 batteries in Parallel ...
littleharbor2 said:There is no "opposite diagonal" connection with a buss bar. Every battery gets it's own cables.
Last I checked everything connects to the buss bar. If anything the loads and charging connections would probably work best at the center of the bussbar.
littleharbor2 said:Last I checked everything connects to the buss bar. If anything the loads and charging connections would probably work best at the center of the bussbar.
It is best to connect the Main Power Cables at opposite diagonals.
Can you explain why?
littleharbor2 said:Can you explain why?
Took me a while to figure out what he was saying too! Connect the cables Main then battery 1, 2, 3, 4, 5,6,7,8 on one side, and batteries 1,2,3,4,5,6,7,8, then main on the other busbar to keep the resistance the same including the busbar.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
I can see that making sense in a minute sort of way. A minute amount of resistance is all it takes to cause uneven charging. I see the buss bar as evenly energized but I'm admittedly no expert. Anybody else care to comment?
My guess is that the connections (battery posts and buss) are likely to be more of a problem than the buss itself in terms of resistance.
In theory, theory and practice are the same. In practice, they rarely are ;-)Off-grid.
Estragon said:My guess is that the connections (battery posts and buss) are likely to be more of a problem than the buss itself in terms of resistance.
Okay good people, thanks for all your replies. "smartgauge" and "iotaengineering" both show the same diagram for a 4-battery string, perfectly balanced. However, I am having trouble imagining how to add the next 4 batteries, to complete a string of 8 batteries. My 2/0 cable is here now, so if someone has a diagram for 8, I will be forever in your debt.
- 218 Forum & Website
- 646 Solar Water Pumping
- 813 Wind Power Generation
- 598 Discussion Forums/Café
- 72 Construction
