Xantrex Freedom HF 1000 and Generators

HuntingCabin72HuntingCabin72 Posts: 5Registered Users ✭✭
I'm looking for some assistance or maybe to offer some advise to someone building a system similar to mine. I have a small 26X26 cabin on a lake and purchased a Xantrex Freedom HF 1000 modified Sine Wave inverter/charger tied to two Trojan 6volt batteries in series. I was running the entire system using a Honda eu20001 inverter generator. Upon first hooking it up I noted that the Xantrex immediately recognized the power supplied by the Honda but would not allow the Xantrex to switch over after the 20 second "test" phase. I contacted Xantrex and was advised that the inverter charger may not like the low power emitted while the Honda was on ECO mode. I then turned the Honda off ECO mode and all was good. Did that for a while and suddenly the Xantrex would recognize the Honda on ECO mode (even better). 
I then upgraded the cabin to include a 1/2 hp Myers jet pump to supply water. However I quickly realized that the 2000 watt Honda could not provide enough power. I did some research and decided on a Firman 3650/4550 watt generator with remote start. I hooked up the Firman as I did the Honda and the Xantrax would NOT recognize the power emitted by the Firman generator. I tried putting a load on the Firman and it would work sometimes and not others. Not only would it not charge my batteries it would not allow the generator power to pass through the Xantrex and power the cabin, it was almost like there wasn't a generator running outside. If I bypassed the Xantrex I had power in the cabin, but once I re-hooked up the Xantrex it would only run off batteries and completely ignore the generator power. 
I contacted Xantrex and they suggested that the frequency of the Firman maybe outside the 60Hz required by the Firman. I noted the Firman posts a 60Hz reading.
I then decided that I would just got back to the Honda and "work around" the pump issue for now, but suddenly the Xantrex won't allow the Honda to switch over in ECO mode. I really don't care about the ECO mode thing, however I would like to solve the power issue as I would like/need a bigger generator, without having to fork over thousands for a larger Honda inverter generator.

Comments

  • EstragonEstragon Posts: 2,594Registered Users ✭✭✭✭
    Maybe try putting a load (eg 60w filament light) on the generator to help stabilize voltage and frequency?
    Off-grid.  
    Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
    Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
  • HuntingCabin72HuntingCabin72 Posts: 5Registered Users ✭✭
    I tried putting a load on the Firman and it would work some of the time. To be clear it was the exact same load each time.
    I did get it to work briefly, then was running a circular saw and managed to overload the plug.. after that the Xantrex would not recognize the Firman.
  • HuntingCabin72HuntingCabin72 Posts: 5Registered Users ✭✭
    I have been doing some reading and “grounding” appears to be a popular issue. I have my cabin panel grounded to a ground plate, I ground the Xantrex to the same ground wire.. Not sure if that is the issue??? Can’t see it, but I’m at my wits end with this.
  • BB.BB. Posts: 27,682Super Moderators admin
    You (generally) cannot ground one leg of an MSW inverter's AC output (to make a ground referenced neutral/white wire).

    If you ground the DC battery (typically negative bus) and an MSW AC output, it creates a dead short through the inverter and lets out the magic smoke.

    Grounding the inverter case to ground wire is correct (aka back to the battery negative bus). If there is a short circuit on the DC bus, this will pop the breaker/fuse.

    The other reason for the ground rod is for lighting safety. (The actual ground rod does not do much useful for 12 VDC or 120 VAC safety).

    Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • HuntingCabin72HuntingCabin72 Posts: 5Registered Users ✭✭
    Bill,
    Thanks for the reply and excuse my electrical ignorance. Are you saying that what I did was correct? Or did I make a mistake?
    Appreciate the assistance
  • BB.BB. Posts: 27,682Super Moderators admin
    You did not really say what you did... The "correct" grounding I would suggest is:
    • Use a 6 awg (minimum) cable from the battery negative bus to the ground rod (keep short and straight, any bends should be nice large rounded corners, and outside the foundation). Hopefully, the battery bus is next to an exterior wall (short, no sharp bends, etc. are if you have lightning in the area).
    • Run a minimum of 6 AWG cable from the housing/chassis of the inverter to the ground rod (same ground rod).
    • If you have a solar panel rack on the roof, the panels+rack should have its own 6 AWG cable from the rack to the same ground rod... If the solar panels are mounted separately from the the cabin, still run the ground cable from the panels to a local ground rod, and run a second 6 AWG cable from the solar ground rod to the cabin ground rod (this is to ground short circuits). If lightning in the area, keep cable from panels frames/rack short and wide bends.
    Grounding should not affect the normal operation of the inverter (properly grounded or not grounded, does not matter).

    When troubleshooting, do you get any other indications of issues (error codes, LEDs, fan running or not, etc.)?

    The Honda eu2000i has very stable frequency and voltage output. However, its ability to start heavy loads (surge current) is not great. In ECO mode (low motor speed), it is even less.

    Do you have an HF1000 or HF1055? The 1055 has 55 Amps of output charging current, and should be dialed back to 20/40 amps with the euc2000i.

    What type/size of battery bank (golf cart batteries/etc., what AH rating is the bank)?

    I guess that you have no AC loads on the inverter when you are trying to qualify the genset voltages?

    When running the circular saw--Did you have it plugged into the genset or the AC inverter?

    The HF-1000 is a relatively small (capacity) inverter, and could not run any larger loads (a refrigerator would be dicey, a circular saw--probably no way from batteries and may damage the inverter if on Genset AC power through the inverter).

    Other inverter issues can happen if your battery bank is too small of AH capacity (recommend at least 400 AH @ 12 volts to "reliably" run the HF-1000 at 1,000 Watt @ 120 VAC load). Also, you can have inverter issues if the cables are too small of diameter (AWG) and/or if you have a long(ish) 12 VDC cable run (need heavy, short cables with good electrical connections to run your DC power).

    Get a DC Current Clamp DMM to help you diagnose/monitor your system. A Kill-a-Watt type meter can be handy to look at your AC loads.

    https://www.solar-electric.com/kiacpomome.html
    https://www.amazon.com/gp/product/B07546L9RT (inexpensive)
    https://www.amazon.com/gp/product/B019CY4FB4 (more expensive)

    Running an MSW (modified Square/Sine Wave) inverter can be hard on some loads... Induction motors do not like MSW. And some things like CFL lightning and many transformer & AC to DC wall warts/computer power supplies/battery chargers/etc. do not like MSW either. Probably 80% of your loads will be OK, and 10% will actually fail or have a shorter life... It is sometimes difficult to tell which load will work or not.

    Note that MSW AC output voltage will read low with Non-True RMS reading volt meters (more expensive). MSW vs PSW/TSW (pure/true sine wave) inverters is a good size subject in itself.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • BB.BB. Posts: 27,682Super Moderators admin
    edited July 31 #8
    By the way, no problem on the questions... We all started at ground zero ourselves and others taught us the basics.

    And I hope we are not frustrating you... Starting in the middle of something that does not quite work is really frustrating for everyone. We are not there, you have an unknown (to us) installation, and we do not know much about your power needs.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • HuntingCabin72HuntingCabin72 Posts: 5Registered Users ✭✭
    Wow.. that’s a lot.. Thanks Again!

    So I have a Freedom HF 1000 watt. My batteries are Trojan T-105 6V in series (2 batteries).
    I have included a picture, the lines coming from the inverter I’ve since been shortened, but the basic instal is the same. The yellow line from the outside wall goes to a receptacle that the generator plugs into, is a 12 gauge 3 prong extension cord, less then 20 feet. The green ground wire on the panel and inverter goes out through the floor to a ground plate directly under.

    When I was running the circular saw the generator was running and it was one of the few times that I had the inverter reading the generator. I had it pulled into an outside 15A plug, not directly to the generator. I was forcing the saw a bit so I get why it tripped, not sure why that shut out the generator.

    There is no large draws on the batteries, my stove is propane, I have LED lights, heat is supplied by a wood stove. The only large draw is the toaster in the morning. No TV, no microwave, very simple and basic. It basically only runs on batteries at night and a bit during tha day if we’re just sitting around having a drink and telling lies.

    There is no warning codes on the inverter it would just have a solid yellow light, showing it’s on battery power, even with the generator running and plug in.

    I did try and put a load directly on the generator (toaster plugged directly into the generator) to try and get the inverter to recognize the power and it did sometimes.
  • BB.BB. Posts: 27,682Super Moderators admin
    A possible grounding issue for the inverter/charger... Some UPS system (uninterruptible power supplies) used with computers need the 120 VAC input to have a ground bonded neutral. If the AC input is floating (no green wire to white wire bond) in the "upstream" AC side, the UPS will not start.

    From the HF manual, it sounds like they may have the same issue:

    http://www.xantrex.com/documents/Inverter-Chargers/Freedom-HF/Freedom HF 1000-1800 Install Guide (975-0395-01-01_Rev-A).pdf (page 25 of the installation manual):
    A source of 120 V, 60Hz sine wave alternating current is needed to provide energy to charge batteries and pass power through to AC loads. This source is usually the utility grid (power company) or an AC generator. An automatic or manual AC source selector switch can be used to switch between the multiple sources of shore power to the Freedom HF system. The AC source feeding the Freedom HF must have the neutral conductor bonded to ground. When the inverter passes shore power through, it will lift the bonding relay on the output and will rely on the input being bonded in order to ensure that the power delivered to a sub panel is properly bonded. See “AC Output Neutral Bonding” on page 1–9 for more information on bonding relay operation.
    Normally, a UPS will report the "missing" AC bond as a fault... Not sure here.

    The eu2000i (as far as I know) has a floating AC output (the two AC leads are "floating" with respect to ground.

    The 3,500 Watt genset probably has the AC White(Neutral+greenwire+frame ground) bonded inside the genset... (My guess is that smaller genset and AC inverters tend to "float" their AC "neutral"--aka no-neutral; and larger gensets--something like 3,000-3,500+ Watt, tend to bond AC White+Green wire+Frame ground at the gest).

    Normally, simply bonding the white wire to green wire somewhere between the genset and the input to your AC inverter is fine... If you are really paranoid (with electricity, it does pay to be careful), use a 20-100 Watt filament bulb to "shunt" the white+green wires together... If the bulb lights (when genset is running), there is something wrong and needs to be addressed before shunting the two wires together directly (should be no power flowing between white and green wires except if there is a problem).

    The other possible issue is your breaker panel... "main panels" generally default to connecting the white wire/neutral bus to the metal case of the panel/box. And the panel box should be connected to your green wire/ground rod.

    Many Auxiliary type panels (and main panels--Talking about North America here--Other countries may have different requirements) will have a configuration connection--Screw in neutral bus that connects to sheet metal box (remove screw, no neutral to ground connection). In your system, the neutral bus should be floating (Not Connected) with respect to the metal box/ground bus.

    Your inverter has a GFI receptacle... If you have a Neutral+Ground connection on the output of the GFI, it will probably trip (this also depends on how you wired the AC output of the inverter. If you wire before the GFI/don't use the GFI, no false ground faults. If you wired your power after the GFI--It has "output" screws for downstream connections, you will probably get false trips if you have a ground+neutral bond in your small AC panel).

    Hope this makes sense... Grounding is a complex subject (note that your inverter has an internal transfer switch which disconnects the neutral from the Genset/AC mains power when the inverter is running--Correct and required for MSW type inverters).

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset