About lightning arrestor

I have to calculate size of lightning arrestor for a solar array may be of 8 panels. Can anyone help me to calculate the height of the rod required. And radius, area of the protection zone. Please help me to calculate this factors, you can explain by taking any example.  Thankyou.. 

Comments

  • mcgivormcgivor Registered Users Posts: 1,281 ✭✭✭✭
    The  mast should be high enough that  45° line from the top to the ground covers the array, more importantly  surge protection devices (SPD) should be installed to protect the electronic components, if the distance between the array and inverter or charge controller is long the recommendation is to install them at both ends, because I know you are powering a pump, I would highly recommend SPD's on the AC side as well. SPD devices are available in both DC and AC, even an indirect strike can produce enough induced voltage to damage equipment.
      1500W, 6× Schutten 250W Poly panels , Schneider 150 60 CC, Schneider SW 2524 inverter, 8×T105 GC 24V nominal 

  • kcbibek310kcbibek310 Registered Users Posts: 13 ✭✭
    is mast a type of conductor? Or we can use any insulator to support lightning arrestor?
  • BB.BB. Super Moderators Posts: 26,837 admin
    What is a "lightning arrestor"? (defining terms here). A lightning rod to intercept the air strike (no insulator involved usually)... Or a surge suppressor to "short circuit" the lightning voltage spike in wiring to ground (usually a device with wiring, many times in a plastic case... Wires to hot circuits + ground wire to earth/metal water pipe/ground rod/etc.)?

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • kcbibek310kcbibek310 Registered Users Posts: 13 ✭✭
    A rod( Spike rod) to intercept the air strike 
  • mcgivormcgivor Registered Users Posts: 1,281 ✭✭✭✭
    The subject of lightning protection is extensive, there are many considerations, to gain some insight, I would suggest reading the links provided, they will answer many of the questions you may have, as well as some not considered.

    https://www.solar-electric.com/learning-center/general-solar-information/solar-system-lightning-protection.html
    https://www.solarinsure.com/protect-your-solar-power-system-from-lightning
      1500W, 6× Schutten 250W Poly panels , Schneider 150 60 CC, Schneider SW 2524 inverter, 8×T105 GC 24V nominal 

  • jonrjonr Solar Expert Posts: 859 ✭✭✭✭
    Some people use a simple 45 degree angle from the tip of the rod downwards.  It's more complicated than this, but probably good enough.