I have a 100 hp pump. I want to use solar to drive it so can u guys help me. Pls tell me the no of battery units configuration panel details kind of panel I want to buy and how much in kw

Comments

  • SolraySolray Posts: 246Registered Users ✭✭
    What is the electrical draw and surge of the motor?
  • mcgivormcgivor Posts: 2,199Solar Expert ✭✭✭✭✭
    You are looking a 75Kw just to run the motor, so let's assume you use a common 250W, 60 cell panel
    The actual output  of such a panel is around 75% of its rated output, 250/.75=187Wh
    75000w/187w= 401, the number of 250W panels needed  just to run the pump under full sun. Depending on location this window of opportunity  could be  very narrow,  so the number of panels would, in all likelihood, have to be significantly higher. Without run times it would be foolish to even speculate on ballance of system requirements, but anything is possible, for starters you would need an 80 Kw DC to AC  3 phase inverter, to take care of the massive inrush associated with such an application. Running without sunlight would probably be cost prohibitive, batteries could be used as a buffer to compensate for passing clouds in a daylight only situation.
    Please furnish us with more details regarding your expectations.
     
    1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery bank 

  • mike95490mike95490 Posts: 7,899Solar Expert ✭✭✭✭
    You are asking about powering a 100 Horse Power pump from solar?   That is a VERY large pump and is beyond the scope of anything I can advise about.  That would require 3 phase power, and at least 480V AC


    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • GaarkuteerGaarkuteer Posts: 2Registered Users
    Thank you for this forum, speaking from Jos Plateau State Nigeria. I really needs help on how to design a circuit of solar without battery that can pump water from a 78m depth borehole and what type of pump will best serve me for irrigation that can pump water atleast 10hrs per day
  • mike95490mike95490 Posts: 7,899Solar Expert ✭✭✭✭
    Without a battery, you will only be able to pump for about 6 hours a day.
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • bill von novakbill von novak Posts: 783Solar Expert ✭✭✭✭
    Thank you for this forum, speaking from Jos Plateau State Nigeria. I really needs help on how to design a circuit of solar without battery that can pump water from a 78m depth borehole and what type of pump will best serve me for irrigation that can pump water atleast 10hrs per day
    How many gallons a day?
  • iyowuna2017iyowuna2017 Posts: 2Registered Users
    Please how many Solar panels will i need to charge a 36v battery
  • EstragonEstragon Posts: 2,838Registered Users ✭✭✭✭✭
    How big is the battery?
    Off-grid.  
    Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
    Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter