Re: Surge Protection Devices - Single Phase and Single Pole - WHY ?
The ground may be bonded to the neutral however the intent is not to provide a path for surge type event such as lightning, it is to provide a path to ground in the event of a ground fault and is si…1 · -
Re: Adjusting a AIMS Model PICOGLF60W24V240VS (6 Kw. 24Volts) Inverter to 50% DoD.
Don't think it's adjustable, what you may want to consider is the amount of energy this inverter needs just being on, without load, 76.8W that's 1.834 Kwh per day or 0.7Kwh in power save mode, seriou…1 · -
Re: Gen low voltage
Can the inverter use 240V as the input voltage rather than 120V, perhaps the imbalance of tapping half the generators output is causing the problem, just a thought.1 · -
Re: Gen low voltage
Loading the generator near it's maximum can cause voltage to drop, high temperature of the windings will compound the problem. By "it" in this sentence "The inverter is set to accept t…1 · -
Re: Cable assumptions
The charging source is different from the dischargeing source, from the battery to inverter use the largest conductors possible, this includes all interconnects, the charging source must have conduct…1 ·