Re: 24v battery setup and charging options for off grid setup
Welcome to the forum @georget Frankenstein, are you planning to create a monster? Seriously bad idea if what's being proposed is to series connecting different lithium sub chemistries of different ca…1 · -
Re: Does anyone know the Amperage rating on Schneider Conext XW PDP DC positive Busbar?
You could measure the thickness and width in millimeters, for example 10mm by 50mm would have a cross sectional area of 500mm^2, multiply by a factor of 1.2A per mm^2 for copper or 0.9 per mm^2 for a…1 · -
Re: Lead Acid Batteries Loud Bubbling While Charging?
Flooded lead acid batteries need to be charged usually at 28.8V at 25°C, perhaps slightly higher, follow manufacturers recommendations. Reducing to 25.5V will result in undercharging, the most common…1 · -
Re: Lead Acid Batteries Loud Bubbling While Charging?
No, the charging rate is specified by the manufacturer, each one varies but it will be a percentage of the Ah capacity, usually somewhere in the 10-20% neighborhood so for example 15% of 100 Ah is 15…2 · -
Re: Confusing Surge Rating Description in my Inverter Manual
Induction motors are particularly hard on inverters because they draw very high current on startup. There are two stages, inrush which lasts approximately 150 milliseconds and surge which is typicall…1 ·