  • Re: Totally lost

    The best place to start is by defining the loads proposed, then build a system to support them. Choosing the most efficient devices possible, is obvious, the use, wether full time living, or occasion…
    ·
  • Re: (un)Realistic AGM specifications?

    If I were you, which I'm not, flooded would be the preferred route to go, maintenance not withstanding, flooded are more forgiving, being easier to understand, the ability to measure the state of cha…
    ·
  • Re: (un)Realistic AGM specifications?

    Whilst doing research, one of the batteries I was looking into was Hoppecke, although the flooded opzs variety which had an impressive cycle claim, even higher than the block AGM, after reading throu…
    ·
  • Re: Installation

    You are looking a 75Kw just to run the motor, so let's assume you use a common 250W, 60 cell panel The actual output of such a panel is around 75% of its rated output, 250/.75=187Wh 75000w/187w= 401,…
    ·
  • Re: MPPT Charge controller setting help :)

    The voltage input maximum for the CC is 100V, although the panel open circuit voltage may be 18-19V, under load, when charging, this will drop, having 2 panels in series will raise the voltage (36-38…
    ·