Re: Schneider XW6848+ and MPPT-60 are displaying different battery voltages
What settings are used on the controller ? Seems odd the voltage discrepancy, try a cold reboot allowing a few minutes to discharge capacitors, nothing to loose. My day has ended, different time zone…1 · -
Re: Schneider XW6848+ and MPPT-60 are displaying different battery voltages
Looking at the figures, this is under battery load, no PV input, what time of day was this snapshot taken? The PV input voltage is 110V not changing, inverter using battery -3.9A, late in the day, or…1 · -
Re: Schneider XW6848+ and MPPT-60 are displaying different battery voltages
What size are the conductors between the controller and battery, how long and what current is the controller displaying? Sounds like a cronic voltage drop problem. Do the conductors between the contr…1 · -
Re: Looking for Suggestions on Combiner box setup for 20 panels in a 48 V system
Charging an EV on a system shared by household system especially off grid could lead to some unpleasant supprises, example bad sun day, it is also inefficient to convert DC to AC then back to DC. The…1 · -
Re: Is automatic equalizing a con?
Not sure the best way to answer that, perhaps get a small 20W panel as a battery minder, not large enough to cause any damage but enough to cover self discharge. I do this on my escavator which sees…1 ·