Re: Solar Charging Seasons
What charge controller are you using? With the Conext 60-150 you could look into history and see if there is a downward trend in production or an abrupt change. Your 25V setting may be on the high si…1 · -
Re: Nearly two days into freshening charge?
Is that voltage taken immediately after charging or after a few hours which will allow the surface charge to dissipate?1 · -
Re: Nearly two days into freshening charge?
What is your interpretation of terminal voltage ? The SG spread is not too high, they may benifit from an EQ, usually an EQ is performed on a new bank even if known to be good, this is part of the co…1 · -
Re: Nearly two days into freshening charge?
What is the difference between the high and low SG cells?1 · -
Re: Nearly two days into freshening charge?
The 2.5A charger would likely be regulated to ~14.4V, which is insufficient to equalize, 15-16V would typically be required.1 ·