Re: Running a 115vac well pump, battery voltage is being pulled down tell inverter shuts off
If the actual, measured at the battery terminals voltage is dropping, then it's not a connection problem,1 · -
Re: AGM Absorb voltage range and temp compensation
I looked at a few AGMs and most were in the range 3-4mv per cell per C. So without an actual number, maybe 18-24mV for 12V. One said 3.3mv for standby, 5.0mv for cycle use.1 · -
Re: Solar rookie seeks help with 15-amp miter saw
If it has a universal motor, it should work to add a 15A dimmer. This would allow a softer start and far less startup amps.1 · -
Re: Off grid electric cooking and opportunity loads
90 watt compressor with COP=3 is 270W of cooling.1 · -
Re: charging battery bank with generator
> what is the best way to wire my batteries for the most even charge However your clamp on ammeter (current in parallel batteries) and volt meter (series balance) shows is most balanced. Start wit…1 ·