Re: EG4-LL LiFePO4 Charge settings
Most BMS balancers do not balance dump a LFP cell less than 3.4vdc. If you always charge to lower voltage you will eventually get out balance cells. You should periodically take absorb to 3.5v per ce…1 · -
Re: Solar Inverter Specifications
The 18A PV input is with a high PV DC voltage panel array input. I am guessing you are talking about a Sol-Ark inverter. Other HF all-in-one inverters operate in simlar way. Sol-Ark has two SCC contr…1 · -
Re: High Frequency Inverters with Split Phase Capability and High Surge Capacity?
Not so much HF vs LF, as it is good design/good quality vs bad design/bad quality, Many of the high freq inverters are very low cost, and low quality. There are only a couple of good quality models. …3 · -
Re: Breaker doesn’t trip but stops passing amps
A breaker will stop the current flow. For breaker on a PV, the panels side will go to Voc and controller side may still show battery voltage. Since it began after adding panels, you may be exceeding …1 · -
Re: SW4024 Trace Inverter
I assume the inverter is locking onto generator. The blinking AC2 LED should turn solid and you hear the relay clunk indicating it connected to generator. If it does not, make sure you don't have cir…1 ·