Re: how much battery cable in conduit?
Re: how much battery cable in conduit? You should have battery +/- cables in pairing together. This help cancel out their magnetic fields. From a single phase AC inverter there will be varying curren…1 · -
Re: Schneider XW+ 6848 AC2 breaker setting
I dislike they changed the name of what should be called AC input current limit to 'AC breaker amperage'. The limit tries to avoid having AC input current exceed the user set limit. This is great whe…2 · -
Re: MPPSolar PIP5048
The setting 38 looks like they incorporated what I was talking about in relay controlled neutral-ground bonding. They put it under user firmware selectable control versus the old way requiring invadi…1 · -
Re: Questions about Trace SW4024 and its grid tie interface
Old SW40xx series use three transformers' series connected outputs to create up to 27 AC output voltage steps to synthesize a sinewave. Because of its stepped sinewave output the inverter by itself d…3 · -
Re: Trace 4024 won't run table saw on new LiFePO batteries
Not sure if you are implying it worked before with lead acid batteries. LFP batteries have greater peak current sourcing, lower series impedance, compared to lead acid batteries. Your problem may be …1 ·