Re: Do we really need an 8kw system just to run an AC unit?!
I would say it's likely that you would need that large a system... 36,000 btu is quite a large air conditioner, from Daikin's web site (trying to find specs), looks like the single head units stop at…2 · -
Re: Production of a 3kw installation
Sounds like no company talked with you about the expected production? Standard Test Conditions (STC) but realistically they produce wattage at Normal Operating Cell Temperatures (NOCT) which is norma…1 · -
Re: PV water heating
Pretty much it's a pure resistance load. It works out that half the voltage (resistance) will max out at 1/4 the power, so a 120v 1500 watt element will max out at about 375 watts at 60 volts. You wo…1 · -
Re: What's wrong with something like this?
What is truly sad about the information, is that they say "... A more economical solution if your inverter doesn’t need a ETL/CSA to UL 458 listing." UL 458 is the standard for Mobile appli…1 · -
Re: ligwyd: Design my the perfect system
If you do it @Estragon's way, be sure to start with the longest runs, and do all the clips and fasteners before you trim the wire. This will ensure you have the shorter wires for the shorter runs.1 ·