Re: Ground rods for pole mount arrays
More or less, you are looking at "UFER" ground (using concrete and rebar to provide grounding). A couple of links to start: https://forum.solar-electric.com/discussion/2650/ufer-grounding h…2 · -
Re: Ground rods for pole mount arrays
I have not look at the NEC in detail for a couple of decades... But, the general requirement is to prevent ground loops "inside the home". And that is done by a single point grounding betwe…1 · -
Re: AIMS 12KW Inverter died.
I have a list of past companies that repair AC inverters... I don't maintain the list--Other than if somebody tells me about another company that is unlisted: https://forum.solar-electric.com/di…1 · -
Re: 24V battery charger recommendations needed
As always, refer to the installation/user manual for your products (I think this is the one): https://powermaxconverters.com/wp-content/uploads/2018/05/PM3-24V-LK-Manual-2018.pdf I like to use NEC wi…1 · -
Re: Cant reach EQ voltage using generator - new batteries
Have you measured the current during EQ? More or less, 5% rate of charge (650 AH [at 20 hour rate] * 0.05 = 32.5 Amp for 5% EQ)... Even down to 2.5% rate of charge can work (16.25 Amps)--Lower charge…1 ·