mix and match panels
BB.
Super Moderators, Administrators Posts: 33,716 admin
We need to know the exact Vmp / Imp of the panels, and how they are configured (parallel, series, series/parallel) and what your battery bank voltage is.
In general, you match Vmp to Vmp within 10% for parallel connections, and match Imp to Imp within 10% for series connections... You will have relatively little power loss.
If you "match" panel voltage/currents way outside the 10% range, you can loose lots of power.
-Bill
In general, you match Vmp to Vmp within 10% for parallel connections, and match Imp to Imp within 10% for series connections... You will have relatively little power loss.
If you "match" panel voltage/currents way outside the 10% range, you can loose lots of power.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Comments
-
Re: mix and match panels
do know that the 10% figures mentioned are somewhat arbitrary as there is some loss within the 10% too. the closer to the current for series and the closer to the voltage for parallel the better and depends on what may be acceptable to a person. personally i feel 10% is too far out, but that's just me. -
Re: mix and match panels
I agree with you niel. I have 1 inverter with 14 Kyocera Kc 158G on one inverter. I had 12 Sharp 167 u3a on other inverter. I put 2 of the kc 158 panels with the 12 sharp and I think the 2 158 watt panels pulled the watts down on the 12sharp 167 watt panels to match them. I have been checking them and the 12 167 watt panels with the 2 158 watt panels are measuring identical amounts of power as the 14 158 watt panels I do have 2 175 watt mitsubushi panels that I am going to try with 12 . the 167 watt panels. Even if the 167 watt panels pulls the watts from the 2 175 watt panels I will still gain power. S:Dlarvicdo know that the 10% figures mentioned are somewhat arbitrary as there is some loss within the 10% too. the closer to the current for series and the closer to the voltage for parallel the better and depends on what may be acceptable to a person. personally i feel 10% is too far out, but that's just me.
Categories
- All Categories
- 232 Forum & Website
- 140 Solar Forum News and Announcements
- 1.4K Solar News, Reviews, & Product Announcements
- 199 Solar Information links & sources, event announcements
- 899 Solar Product Reviews & Opinions
- 256 Solar Skeptics, Hype, & Scams Corner
- 22.5K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.6K Off Grid Solar & Battery Systems
- 428 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 656 Solar Water Pumping
- 816 Wind Power Generation
- 624 Energy Use & Conservation
- 620 Discussion Forums/Café
- 313 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed