I have (4) 63W (VOC17v?) panels that are older and am buying (4) new 208W (Voc37V?).
Can I somehow use all of these panels together in the new system? Maybe an old panel and a new panel in a string? Then the string in parallel?
Kim
Kim
Re: Mixing panels
What is the Vmp/Imp of the panels and what battery bank voltage? I assume you are currently running a smaller PWM type charge controller.
We need to know Voc (voltage open circuit) so that we don't over voltage the charge controller-but we need Vmp to make sure that it is high enough to charge the battery bank and make sure that we match within 10% of their Vmp voltage when connecting them in series.
Need to know your battery bank voltage (12/24/48 ) to figure out the Vmp>Vbatt+2 volts or so.
By the way, you are adding a new MPPT controller for the new panels?
If you end up with two controllers--it may be easiest to leave the existing panels on the small PWM controller and just setup the array for the 205 watt panels on the new controller.
Re: Mixing panels
Sorry.
They are feeding an unknown controller (still trying to figure out if one is there already or if we have to order one) to a 12V battery bank. I assume the Vmp is similar to the Voc. The panels are poorly mismatched in terms of V's.
63W (Voc = 17v?) panels that are older and am buying (4) new 208W (Voc = 37V?). -
Re: Mixing panels
With a 12 volt battery bank and a Vmp or Voc = 37 volts--you are going to have to use an MPPT charge controller.
Perhaps I should move this thread into your other thread?
I am sorry--but it is easier for my poor old brain if the details of the system design are in the same thread as the questions--or at least in this thread give us the basic system setup (I know that one thread with 10 different discussions about your system can be confusing to you)...