Suggestions for off-grid island home in Maine
Comments
-
Re: Suggestions for off-grid island home in Maine
From the PV Watts website--1,520 watts of solar panels fixed and 2-Axis in Caribou, Maine (derating factor = 0.52, all else using defaults):[FONT=Fixedsys]Results fixed 1,520W off-grid array Caribou Main Month Solar Radiation (kWh/m2/day) AC Energy (kWh per month) Energy Value ($ @ 12.2 ¢/kWh) 1 3.36 87 10.61 2 4.34 101 12.32 3 5.23 131 15.98 4 5.75 135 16.47 5 4.99 112 13.66 6 5.09 108 13.18 7 5.15 110 13.42 8 4.99 109 13.30 9 4.26 93 11.35 10 3.45 80 9.76 11 2.38 54 6.59 12 2.73 70 8.54 ======================================= Year 4.31 1192 $145.42 [/FONT]
And:[FONT=Fixedsys]Results 2-axis tracking 1,520W off-grid array Caribou Main Month Solar Radiation (kWh/m2/day) AC Energy (kWh per month) Energy Value ($ @ 12.2 ¢/kWh) 1 4.08 107 13.05 2 5.30 125 15.25 3 6.48 165 20.13 4 7.64 183 22.33 5 7.13 166 20.25 6 7.66 170 20.74 7 7.10 158 19.28 8 6.74 152 18.54 9 5.43 122 14.88 10 4.11 97 11.83 11 2.73 63 7.69 12 3.29 85 10.37 ======================================= Year 5.64 1592 $194.22 [/FONT]
Assume months May thru September:
Ave: 106 kWhrs per month (5 month average for fixed array)
Ave: 156 kWhrs per month (5 mn ave for 2-axis tracking)
(156 / 106) * 1,520 watt array = 2,234 Watt effective if 2-axis tracking
Assume $4 per watt (shipping + taxes):
( 2,234 - 1,520 ) * $4 = $2,860 worth of "extra solar panels" vs "2-axis tracking"
So--the difference in power output between a 2-axis tracker or just purchasing and installing more solar panels for Caribou main is $2,680 -- So what does a 2 axis tracker cost to install vs installing more panels on a fixed array?
Assuming $1 per watt for fixed array hardware:
2,234 Watts * $1 per watt = ~$2,234 for fixed array mount
1,520 watts on a 2 axis tracker cost less than $2,234+$2,860=$5,094 ?
Plus labor, materials, hole in ground, etc. for installation...
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Suggestions for off-grid island home in MaineIsland Mon,
12 x 210 W = 2,520 W STC. This value pushes the FM80 beyond its spec limit. Reconfiguring the array from “48 V” ( 4 modules in series x three parallel strings) to “36 V” (3 modules in series x 4 parallel strings) will improve the FM80’s operating efficiency and therefore reduce waste heat. The “36 V” array’s summer voltage will still be high enough to achieve battery voltage targets for a 24 V system.
See: http://www.outbackpower.com/pdf/specs/flexmax.pdf
And: http://www.evergreensolar.com/upload/011108%20Datasheets%20(SR)/ES-A_200_205_210_US_011108.pdf
HTH,
Jim / crewzer
Hi Jim, I am now planning on going with a 48V battery bank, 16x trojan L16H's. I am not clear on how the FM80 will not suit my needs. I see on the attached document that you gave me, max system voltage 150VDC, max solar array STC nameplate 48V 5000 watts, can charge a 48V battery bank..etc.
What am I missing?
If you could explain I would appreciate it very much!
Island mon -
Re: Suggestions for off-grid island home in Maine
"Assuming $1 per watt for fixed array hardware:
2,234 Watts * $1 per watt = ~$2,234 for fixed array mount
1,520 watts on a 2 axis tracker cost less than $2,234+$2,860=$5,094 ?
Plus labor, materials, hole in ground, etc. for installation...
-Bill "
Nice data Bill !
I would run your numbers with a single axis as the dual axis units are for grid-tie in my opinion. More to maintain and the key to offgrid is not the total watts but rather completing the charge as well as reducing the hours that you are using the battery each day! Trackers make the battery you have appear larger not to mention more days that will complete charge which increases battery life.
The intangibles are huge offgrid!"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Re: Suggestions for off-grid island home in Maine
Here are the results for a 1-axis tracker:[FONT=Fixedsys]Results 1-axis 1,520W off-grid array Caribou Main Month Solar Radiation (kWh/m2/day) AC Energy (kWh per month) Energy Value ($ @ 12.2 ¢/kWh) 1 3.84 101 12.32 2 5.12 121 14.76 3 6.36 162 19.76 4 7.34 175 21.35 5 6.49 150 18.30 6 6.74 149 18.18 7 6.47 143 17.45 8 6.36 142 17.32 9 5.30 118 14.40 10 4.07 96 11.71 11 2.68 62 7.56 12 3.06 79 9.64 ===================================== Year 5.32 1498 $182.76 [/FONT]
May-Sept average: 140 kWhrs per month
vs 106 kWhrs per month for fixed; and 156 kWhrs per month for 2-axis
(140 kWh per mnth / 106 kWh per mnth) * 1,520 kW array = 2,010 fixed mount equivalent array...
Note that these advantages for tracking arrays over fixed seem to almost disappear for winter (poor weather and/or poor sun angles?). So--for winter you still may be left with the choice of more panels and/or more generator use...
-Bill
PS: Dave, I do agree with your observation that if you need power during "summer" daylight (such as A/C, shop equipment, etc.)--that trackers do off-load the batteries somewhat as the panels continue to support loads better at the beginning/ending of the day vs fixed mount arrays.Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Suggestions for off-grid island home in MaineBattery Bank:
24Vdc 12x Trojan L-16H, 420Ah (20hr)
3 strings of 4 in series, total of 24V 1260Ah
I will have the positive(+) and negative(-) cables from each string attached to two bus bars.
I will be discharging no more than 25% of total capacity. Estimated storage of roughly 2 days.
Inverter:
24V 4000watt Magnum inverter 120/240Vac split phase.
-or-
two outback FX2524T's 24V stacked. Providing 120/240Vac
Your earlier post indicated that you were planning a 24 V system. It's this nominal system voltage for the battery bank and inverters that determines what size array the charge controller can handle. The FM80's limit for 24 V systems is either 2,500 W STC or 2,000 W STC, depending on if the NEC 690.8 is applied
If you've changed your system configuration from 24 V to 48 V (nominal), then the FM80 will handle an ~2500 W STC array with ease. In fact, you'll find the FM80 crewzin' along at ~97.5% efficiency operating in bulk mode in the summer with the array supplying ~2,000 W at ~74 V operational Vmp. Please see the attached chart.
But, the array configuration will get a bit more complicated. Specifically, using flooded-cell batteries from Rolls/Surrette or Trojan, I'd recommend that you configure the array with five ES-A modules in series for each string. The winter Voc won't be too high (per NEC 690.7), and the summer operational Vmp (less than STC Vmp) will be high enough to achieve battery voltage charging targets while overcoming voltage drops in the wiring and inside the charge controller.
HTH, and please let me know if you have any further questions.
Regards,
Jim / crewzer -
Re: Suggestions for off-grid island home in MaineIsland Mon,
But, the array configuration will get a bit more complicated. Specifically, using flooded-cell batteries from Rolls/Surrette or Trojan, I'd recommend that you configure the array with five ES-A modules in series for each string. The winter Voc won't be too high (per NEC 690.7), and the summer operational Vmp (less than STC Vmp) will be high enough to achieve battery voltage charging targets while overcoming voltage drops in the wiring and inside the charge controller.
Jim / crewzer
Thanks for your help Jim,
The structure that I am putting my panels on can only fit 12 of the evergreen panels. I was planning on combining the series strings of 4 via combiner box and running a pair of 1/0AWG cables down 20-30 ft to the charge controller. Using the 1/0 cable I would be keeping the voltage drop well below 3%.
My concern is, I do not have a large enough roof structure to have 15 panels (3 strings of 5 in series). My only other option is taking away two panels and having two strings of 5.
Will 3 strings of 4 in series not supply enough voltage during the summer months? Keep in mind that avg high temps are in the high 70's.
Thanks,
Island Mon -
Re: Suggestions for off-grid island home in MaineWill 3 strings of 4 in series not supply enough voltage during the summer months? Keep in mind that avg high temps are in the high 70's.
I consider both the “bottom end” and the “top end” when addressing this issue.
At the “bottom end”, Trojan says 59.2 V is required for the end-of-bulk absorb target, and 62.0 V is required for the EQ target voltage. These targets are for batteries at 80 F; colder batteries need higher voltages. At 70 F, figure on increasing each target voltage by ~0.6 V, so 59.8 V and 62.6 V respectively.
See: http://www.trojanbattery.com/BatteryMaintenance/Charging.aspx
Adding in ~2 V for losses in the wiring, breakers, and terminals (~3%), and another 2 V for the voltage drop inside the controller’s DC-DC converter, the gross targets measured at the array may be ~63.8 V and 66.6 V.
At the “top end”, the ES-A 210 module’s STC Vmp spec is 18.7 V. This spec is based on a module cell temperature of 25 C, or 77 F. However, summer-mid-day module temps are typically 25 C (pole mount) to 35 C (parallel roof mount) or so higher than ambient. Assuming 25 C (~77 F) ambient and a 30 C cell temp rise, the module cells will operate at ~55 C, or ~30 C above STC conditions.
Evergreen’s NOCT specs provide a glimpse into this behavior. The NOCT specs (80% insolation and 20 C ambient) indicate cell temperature of ~45 C (25 C above ambient) and an operational Vmp of 17.0 V.
See: http://www.evergreensolar.com/upload/011108%20Datasheets%20(SR)/ES-A_200_205_210_US_011108.pdf
Evergreen’s temperature coefficient for module Vmp is -0.43%/C. At 30 C above STC spec, the module Vmp should be 18.7 V x ~87%, or ~16.27 V. Four modules in series will supply 65.1 V. This value will likely be further reduced if the array is roof mounted and/or mid-day ambient temperatures exceed “the high 70’s”.
My view is that the calculated 65.1 V operational Vmp is too close to the 63.8 V and 66.6 V targets identified above. The result may well be a system that works satisfactorily part of the time, but will likely struggle if the array is roof-mounted, when ambient temperatures are high, and/or when it’s time to EQ the batteries.
This is an example of why I’m such a fan of “60 V” array applications for systems with 48 V flooded-cell batteries.
HTH,
Jim / crewzer -
Re: Suggestions for off-grid island home in Maine
Jim, thank you for a very thorough explanation.
I know that I mentioned using Trojan L-16's, however, what if i chose to use a similar 6v AGM battery. I see that the daily charge rate is between 55.2-56.4V and the float charge is 52.8V.
I assume the AGM's will be compatible with the FM-80
I understand what you are saying, but I am trying to keep strings of 4 in order to keep my setup of 12 panels. I cannot fit any more than 12 panels on the roof, hence why I am being so difficult.
Thanks in advance.
Island Mon -
Re: Suggestions for off-grid island home in Maine
Island Mon,
AGM's change the picture considerably! Assuming an end-of-bulk/absorb target voltage of ~57 V at 77 F, you should be fine, especially since EQ is typically not required, although Concorde's tech manual discusses otherwise.
I've been using East Penn Deka (also known as MK) AGM batteries for several years, initially with the MX60 controller, and now with an FM80.
You can read more about my experiences with AGM batteries from these discussions on the OutBack Forum:
http://www.outbackpower.com/forum/viewtopic.php?f=1&t=848
http://www.outbackpower.com/forum/viewtopic.php?f=1&t=1750
BTW, have you already purchased the Evergreen modules? There may be other products that, configured as 4 x 3 or 3 x 4, will work "more comfortably" with flooded-cell batteries.
HTH,
Jim / crewzer
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed