Homegrid Battery compatibility with XW+6848 and InHome Gateway?
ELYNN4
ELYNN4 Registered Users Posts: 155 ✭✭
I’m running in to issues with installing the Homegrid batteries.  In order for the InHome Gateway to communicate with the Homegrid batteries the Gateway firmware must be updated to v1.18.  The XW+ 6848 does not get along with v1.18.
Wondering if anyone has found a workaround for this issue?
Thanks in advance for any suggested solutions!
Off Grid, 4.5KW array, 9&6KW Gens, 6848XW inverter, Midnite Classic 150, 2 strings - 48V - Trojan FLA L16 2V, located in Talkeetna, Alaska
  • ELYNN4
    I’ve learned from Schneider that the XW+ will not support closed loop operations with an external BMS.  At this point it looks like I am stuck with using the Homegrid batteries in an open loop configuration.
    Dave Angelini Solar Expert Posts: 7,091 ✭✭✭✭✭✭
    Pretty common problem these days. Schnieder has a list of support for closed loop. Discover is seamless.
    Hopefully you can get Soc directly from the Homegrid BMS?
  • ELYNN4
    Hi Dave, yes I can get SOC, but will probably go with voltage parameters for setting AGS triggers.
    Yes you will have to use voltage. Just be conservative or the BMS may shut down power.