MPPT controllers and cheap solar panels
cptdondo
Solar Expert Posts: 104 ✭✭✭
I just bought a 2018 Airstream Basecamp. It comes with 2 ZAMP 80W "12V" panels, wired in parallel. Airstream used the cheapest solar controller possible; an Atkinson that basically closes a relay when the Vcc on the panels exceeds the battery voltage.
The wire from the panels looks to be pretty thin; maybe 14GA.
I want to add a 3rd panel, for a total of 240W. Looking at similar panels, I'm gonna guess this one is the closest:
https://www.solar-electric.com/solarland-slp080s-12m-70-watt-12-volt-solar-panel.html
So.... I want to rewire the panels in series, so the max current in that thin wire is less than 5A. Voc would then be ~60V for all 3 panels.
I want to use a Victron 100/30 MPPT controller:
https://www.solar-electric.com/victron-energy-smartsolar-mppt-100-30-charge-controller.html
Anyone see any issues with that?
The wire from the panels looks to be pretty thin; maybe 14GA.
I want to add a 3rd panel, for a total of 240W. Looking at similar panels, I'm gonna guess this one is the closest:
https://www.solar-electric.com/solarland-slp080s-12m-70-watt-12-volt-solar-panel.html
So.... I want to rewire the panels in series, so the max current in that thin wire is less than 5A. Voc would then be ~60V for all 3 panels.
I want to use a Victron 100/30 MPPT controller:
https://www.solar-electric.com/victron-energy-smartsolar-mppt-100-30-charge-controller.html
Anyone see any issues with that?
Comments
-
Not really... Only two question that could do with a little further research--What is the 14 AWG cable runs length from panels to solar charge controller, and what is the run length and wire AWG from solar charge controller to battery bank.
Ideally, you would like 3% or less voltage (power) drop in the panel to controller wiring (with MPPT panels and several in series--Your system would work just fine with >>3% voltage drop, you just lose that power as wire heating instead of charging battery bank (I.e., 10% or ~5.4 volt drop, you would lose about 10% of your solar array output on a sunny/clear day with max battery charging (bulk charging).
On the wiring side from controller to battery bank, for a 12 volt battery bank you would want around 0.05 to 0.10 volt Max drop... This ensures that the controller is "seeing" the correct battery voltage and is charging optimally. Too much voltage drop, then the battery charging voltage ls lower, and reduced current flow, battery bank ncharges slower.
You could use a voltage drop calculator (one way wire length, working voltage, and max sustained current--Like this one):
https://www.calculator.net/voltage-drop-calculator.html
Other things... MPPT controllers (really any electronics) should be installed in an area with good cooling... Running hot, or lots of min/max temperature cycling causes shortens life for the electronics (and "hot" MPPT controllers can reduce current output to prevent overheating).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed