XW6048 with 2 MPPT60-150 charge controllers - one controller now gets F71 Battery Over Current
pcguy2u
Solar Expert Posts: 151 ✭✭✭
All
of a sudden after years of pretty normal operation, I get fault F71 on MPPT60
00, the circuit breaker trips and the 00 controller screen goes blank.
Flipping the breaker immediately brings it back to life and it happens
again in a few days. The other breaker, presumably for MPPT60 01, never
trips during the time the 00 controller is off, or anytime.
I
assume that this is a wiring issue and have checked/tightened all the
lugs just a few moments ago (and read the related thread), so not sure if that has had any effect.
Also, the fault message says MPPT60 00 but as I think about it, this is
after the event and I'm not sure if the 00 controller is actually the
problem or not since the system views the controller as 00 when there is only 1; base zero and all.
Have also checked the voltages in and out of all the connection and there are no glaring differences. Everything looks pristine, just like new...
Checked the lugs under the controller access cover and snugged them up a bit. Too soon to tell.
One
thing that bothers me about the system is that from day one, MPPT60 00
has consistently read lower on the SCP than the 01 controller. For
example, right now at al most 11AM the 00 controller reads about 30A and
the 01 reads about 41A and the watts readings vary likewise (00 gets a bit more sun early and 01 gets more late). The input voltages are also the same and read 107VDC+- with a DVM, but the SCP meters do not seem to coincide. Just now read the SCP and 00 read 19A @ 106, while 01 read 23A @ 101. Not sure
if there correlation to the problem here, but this is a bit
A couple of pics; the breaker that trips is always the one on the very left:
Any thoughts?
Many thanks, Nick
Comments
-
Here's an update to the PV input numbers (SCP meter readings) provided above from just before 11AM.00 19 10601 23 101And now at 11:45AM00 22 10601 25 102But the input voltages on the back side of the breakers both read the same and were both 107+- much earlier this morning ???
-
And I just checked the temperatures on the controllers and the wiring in the distribution box. In particular, the battery connections going into the circuit breakers are different, even though they are both less than a foot long and are lugged on to the same bus. 00 was 86f and 01 was 76f on the input (upper) side. On the output side (lower) they were the same.The controllers were not the same; at a point just above the case where the cooling fins start at the center of the box: 00 was 116f and 01 was 111f.Ambient was/is 51f and most everything else was not too far above ambient.
-
Probably a breaker is marginal. Swap the breakers to test this."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Thanks Dave, thought about that but planned to see if it's less time consuming and cost effective to just buy a new one? Need to find a source for the proper breaker first...
-
The store here has them and it is a good thing to buy from them, in many ways. I use them alot of the time for certain clients."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Overnight, while it was dark, started by removing/testing the two one foot cables from the positive battery buss to the breakers in question. Both tested normally, even under twisting/torqued conditions. So I reinstalled them and put them on the opposite breaker. The issue of the two arrays/charge controllers producing significantly different outputs is now much less obvious and as the day progresses, the difference changes with the position of the sun, as it should. Now at the end of the day, the controller getting the more direct sunlight produces the greater output. I'm not totally sure, but it also seems that the "sell to grid" event occurs earlier??? The event log does not go back far enough to make a comparison... :0(Also, the temp differences on the breaker/cable lugs have now largely disappeared.More to follow, Nick
-
While this has not happened again, it is nonetheless troubling. Primarily because of the differences between the input (charging voltage) on the lower side of the two breakers on the left, and the output side. Also, the temp difference between the two cable connectors on the top of those same two breakers is confounding. As reported above I removed the two and tested them but not under load; I should have use a battery load tester with each of the short connectors in series and I may do that. Now the one with the higher temp reading has moved from the one on the left to the one on the right, although the difference is not glaring as it was previously.Dave, what was the basis for your decision to replace the breakers you referred to above? Do those breakers have an internal resistance originally?TIA, Nick
-
It is a simple thing to do ! Basic troubleshooting. Eliminate a problem source that is easy to do.
Since I do not know the amp rating of the CB, it just was an easy call for me as you could be overthinking this.
Could also be a mosfet that is intermittent.."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
I periodically see the same error, but it clears quickly, and no breaker tripping. The attached panels can't possibly drive it over current.
-
I have been checking the charge controllers daily to date and have found no evidence of this recurring.
-
twistedtree said:I periodically see the same error, but it clears quickly, and no breaker tripping. The attached panels can't possibly drive it over current."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Dave Angelini said:twistedtree said:I periodically see the same error, but it clears quickly, and no breaker tripping. The attached panels can't possibly drive it over current.
-
You are good then as there has not been much reason to update the old mppt-60.
Check your wiring ! Check your network wiring! Use the raceways designed for network cables."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
I got two mppt60s too. Just got the coldest day of the last few years. So one of the mppt60 units has a fault from dc input over voltage. At the moment it says 145.2 volts. I can open all pv breakers, disconnect the dc output, display goes dark. Then when I power everything up the fault persists. Even with the gateway/insight, I reset the fault, all the faults, reboot, go into standby, and back to operate. There is nothing I do that will restore this unit to production.
Anybody got any ideas ? It's been running fine for years and years. We all know the colder the panel gets the more output it has.
hybrid: xw6848 pro with two mppt60, 6 kw pv
17 cell 280ah LiFePO4 storage 14 kw
gridtie: sunny boy sma 2x 5k
gridtie: fronius ag5100 5k
Gateway / Insight Local
xw4548 backup -
What is the actual voltage on the input with a external voltmeter on a cold morning? Sounds like your array design did not account for low temps.
DC disco on both I/O on mppt for 5 minutes. Measure DC for zero vdc before you connect DC.
Go Tampa against the Lions today ! I want you guys over Detroit next Sunday.
"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
It appears that playing with the actual buttons on the device, got me a reset. No reason why the Insight clear was ignored. It'll take more than one prayer for the Bucs to make it.hybrid: xw6848 pro with two mppt60, 6 kw pv
17 cell 280ah LiFePO4 storage 14 kw
gridtie: sunny boy sma 2x 5k
gridtie: fronius ag5100 5k
Gateway / Insight Local
xw4548 backup -
Were you trying a clear with Insight Local or Insight Cloud?
You have a great coach ! I know 3 49er fans that are praying for the Bucs today! See you next Sunday 🤞
\
"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Insight Local
- Version: v1.14
- Build number: 488
hybrid: xw6848 pro with two mppt60, 6 kw pv
17 cell 280ah LiFePO4 storage 14 kw
gridtie: sunny boy sma 2x 5k
gridtie: fronius ag5100 5k
Gateway / Insight Local
xw4548 backup -
I have three separate JKBMS modules on 3 different banks of Lithium cells. Do we have to worry about the BMS device pulling and pushing 2 amps between cells when the temps are below 32F ? I don't think the board senses temperature at all. I have the 24 cell model with no disconnect, just active balancing.
hybrid: xw6848 pro with two mppt60, 6 kw pv
17 cell 280ah LiFePO4 storage 14 kw
gridtie: sunny boy sma 2x 5k
gridtie: fronius ag5100 5k
Gateway / Insight Local
xw4548 backup -
Check the battery manuals and see what their limitations are...
I would suspect that any "balancing" current (charging) with sub 32F is damaging to Li Ion cells.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed