mppt 60amp enough
robocop
Registered Users Posts: 118 ✭✭
Hi
I have here a mppt 60 amp to charge 12 12v 250ah gel batteries.
inverter is 110vac . 3kw
think mppt 60 a is not enough to charge during the day (tropic 6 hours of sun)
Or do I need a 120a to charge those gel batteries
appreciate your comments about this
Bob
I have here a mppt 60 amp to charge 12 12v 250ah gel batteries.
inverter is 110vac . 3kw
think mppt 60 a is not enough to charge during the day (tropic 6 hours of sun)
Or do I need a 120a to charge those gel batteries
appreciate your comments about this
Bob
Comments
-
You can estimate how long the charging will take with this equation:Battery Qty*battery V*battery Ah / controller A*VThat is to say, 12*12.8V*250Ah / 60A*12.8V = 38400/768=50hConsidering the power loss during working, the actual timescale will be longer than the result.So I think you can consider a bigger controller.
-
You need to look at the charging current specification in the GEL Battery's manual... Some are rated for a relatively low charging current of like 5% rate of charge... Others can accept higher current.
We also need to know if this is a 12/24/48 volt battery bank system... To take a guess:
12 batteries * 12 volts * 250 AH per battery = 36,000 WH battery bank
36,000 WH * 10% rate of charge = 3,600 Watts of charging power
3,600 Watts of charging power * 1/0.77 panel+controller deratings = 4,675 Watt array (nominal 10% rate of charge)
A 60 Amp MPPT charge controller can charge a battery bank at with a typical "over sized" PV array:
12 volt bank:
14.5 volts charging * 60 amps * 1/0.77 panel+controller derating = 1,130 Watt "Max cost effective" array
24 volt bank:
29.0 volts charging * 60 amps * 1/0.77 panel+controller derating = 2,260 Watt "Max cost effective" array
48 volt battery bank:
58.0 volts charging * 60 amps * 1/0.77 panel+controller derating = 4,519 Watt "Max cost effective" array
So to even get a 10% rate of charge into your 12 batteries, you would need have a 48 volt battery bank.
If you were are going for a 5% rate of charge, then a 24 volt battery bank with a ~2,260 Watt array would meet that requirement on a single 60 amp MPPT controller.
In any case--We do need more information--Such as how deeply you discharge your battery bank every day--Or daily loads, battery bank voltage, etc... to give a "better" answer.
GEL batteries are frequently not a very good option for solar power systems... They, typically, have a lower charge rate acceptance than flooded cell or AGM (for lead acid batteries). So you cannot discharge them very deeply because of limited hours per day to recharge.
Flooded cell and AGM batteries accept higher charging current (10%-20% or 25%)--So you can charge them more quickly when more deeply discharged. SOME GEL batteries can be damaged by higher charging current (gassing causes bubbles in GEL, which don't go away--Limiting electrolyte to plate contact area.
10% rate of charge is the typical suggested minimum rate of charge for an off grid system... Being in the tropics with lots of sun all year round--sometimes can get away with less than 10% rate of charge (again, guessing without knowing your loads).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
forgot to write 12 batt of 250ah in 3 battery bank of 48v
-
Does your battery manual list a maximum rate of charge for your batteries?
What size solar array do you presently use?
Are you able to recharge the battery bank to 80-90%+ State of Charge at least a couple times a week (based on your loads and amount of available sun) with your present system--Or do you need more charging energy?
3x 250 AH strings = 750 AH total
60 amps / 750 AH = 0.08 = 8% rate of charge (assuming at least 4,519 Watt array in full sun)
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
for information . am using now 4pcs 500w in 2s2p configuration
-
- 2,000 Watt array * 0.77 panel+controller derating * 1/58 volts charging = 26.6 Amps "typical best case" charging current
- 26.6 Amps / 750 AH battery bank = 0.035 = 3.5% rate of charge
In the end, your 60 amp MPPT charge controller is not the limiting element of your current system. Unless your actual daily Watt*Hour usage is very low, you really need more panels, and probably another charge controller...
Again, depending on your daily energy usage.
On average, most battery banks die from under charging/over discharging. More charging should give you longer battery bank life.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed