Schneider 4048 f1 AC Output Under Voltage
cmsolera
Registered Users Posts: 4 ✭
i have an Schneider 4048. During startup, the mode is inverter, and theres a popup, showing AC Output Under Voltage.
Is the popup warning temporary (goes away after inverter has started)?
Have you measured the DC input voltage to the AC inverter and it the input voltage is staying above ~42 VDC?
The error reset and then it start again to try to start the inverter and the fail again. The voltage during the startup is about 55 to 51, because the solar panels are supply maintained the voltage.
Sounds OK... What is the battery bank AH rating (type of batteries, etc.)? For flooded cell lead acid batteries, typically suggest a 4,000 Watt @ 48 VDC inverter should have a minimum of 400 AH @ 48 volt FLA battery bank.
Should add that need to have relatively heavy/short cables from battery bank to carry the current:- 4,000 Watts * 1/0.85 AC inverter eff * 1/42.0 volts battery cutoff voltage = 112 Amps max continuous current @ full load
In this moment i have a 48v bank with 250ah gel battery
Should not cause a term/startup issue (assuming good quality GEL batteries).
DC wiring AWG and length from battery bank to inverter DC input.
DC wiring is good. The system work without problem at the beginning of the installation, the problem begins after a maintenance shutdown.