off grid system for shop and home
tec77
Registered Users, Users Awaiting Email Confirmation Posts: 1 ✭
i keep looking for simple plain English set ups I've had 6 estimates for solar and the last was from sun solar here in MO of 64000 and still being tied to grid no batteries only generator backup i do not want tied to grid electric coop does not pay me back for power i over produce and refuses to help me out in anyway secondly i do not want a payment thats over twice what my electric bill is ,my electric coop has upped meter fee / point of use fee to 49 a month and raised rates so off grid here i come so im looking for advice i found tested used panels for decent price i plan on lead acid batteries that are recyclable yes i know not as efficient but can get long life out of with reg service trying to figure out how many i need for my system solar guys told me a 22kw system max ive used in a month is 1800kw
If you are serious about off grid, want a reliable quality system and if you are a handy person, I suggest that you give Dave Angelini (on this forum) a shot.I used Dave’s services and it’s worked out well.Best.Off-Grid in Terlingua, TX
5,000 watt array - 14 CS 370 watt modules - 7S2P. HZLA horizontal tracker. Schneider: XW6048NA+, Mini PDP, MPPT 80-600, SCP. 650ah LiFeP04 battery bank - 5 Discover AES 42-48-6650 48 volt 130ah LiFePO4 batteries -
When going off grid solar, I always suggest conservation first. Lots of insulation, double pane windows, possibly heat pump HVAC, etc...
A full off grid system, very roughly, costs around $1-$2+ per kWH for full time off grid (all the hardware costs, battery replacement every 5-7 years of so for "average" FLA batteries, etc.). One person here is probably down to $0.50 per kWH through finding good prices, self install, and carefully managing his loads (even some AC in summer)...
Anyway... I will go through the quick math for a "nominal" system design (Lead Acid batteries, our common d design rules).
Normally I would be suggesting a 100-300 kWH per month system as an aiming point. But I will use your 1,800 kWH per month. Assuming 2 days of storage (bad weather support) and 50% planned max discharge (for long battery life).- 1,800 kWH per month / 30 days per month = 60 kWH per day = 60,000 WH per day
- 60,000 WH per day * 1/0.85 AC inverter eff * 2 days storage * 1/0.50 max planned discharge * 1/48 volt bank = 5,882 AH @ 48 volt battery bank
- 5,882 AH * 58 volts charging * 1/0.77 panel+controller deratings * 0.05 rate of charge = 22,153 Watt array minimum (summer/weekends)
- 5,882 AH * 58 volts charging * 1/0.77 panel+controller deratings * 0.10 rate of charge = 44,306 Watt array nominal
- 5,882 AH * 58 volts charging * 1/0.77 panel+controller deratings * 0.13 rate of charge = 57,598 Watt array "cost effective" maximum
http://www.solarelectricityhandbook.com/solar-irradiance.htmlColumbia
Measured in kWh/m2/day onto a solar panel set at a 51° angle from vertical:
Your energy usage varies by season (A/C, Heating, etc.)... Using December as "break even month":Jan Feb Mar Apr May Jun 3.36
3.67
4.49
4.91
5.03
5.28
Jul Aug Sep Oct Nov Dec 5.48
5.34
5.17
4.48
3.35
3.11
- 60,000 WH per day * 1/0.52 off grid AC system eff * 1/3.11 hours of sun per day (December) = 37,101 WH array December break even
- 37,101 Watt array * 1/0.65 fudge factor = 57,059 Watt array for December w/ fudge factor
Lots of room for adjustments based on what your "real" power needs (by season) and if you can do some significant energy conservation.
You can plug in your values and do some what ifs and paper designs and see what works for you.
Your thoughts?
