what would happen ?

Options
Spacedinvader
Spacedinvader Registered Users Posts: 1
i have a 24v inverter what would happen if i hooked a 12v inverter up to the one of the female ports that is 12 volts ? i know the inverter is expecting dc but would it matter ? hurt the device ? rather ask the pros b4 i burn something up 
Thanks in advance 
Tagged:

Comments

  • BB.
    BB. Super Moderators, Administrators Posts: 33,439 admin
    Options
    Welcome to the forum SapcedInvader,

    In general, the issues are... If you have a 24 VDC battery bank and draw 12 volts from 1/2 the battery bank. It will "discharge" the first time fine... But you will end up with the "high 12 volt" bank and the "low 12 volt" bank with different states of charge--And it will be difficult to get both battery sets back to full charge without damaging one of the 12 volt banks.

    Not to say that this cannot be done. There are ballancers that will take power from the full charge bank and use it to charge the discharged bank. This is not uncommon in the RV industry where you may have a 24 volt chassis battery (run the coach chassis power) and 12 volts to run the "house" power (12 volt inverter, 12 volt lights, 12 volt appliances).

    There are devices that can drop the 24 VDC DC power to 12 VDC (to run 12 volt appliances)... Just be aware that inverters typically draw a lot of current (i.e., 600 Watts @ 120 VAC or 5 amps; will draw >50 amps from the 12 VDC bus).

    Cannot really give you specific answers without knowing more about your power system (24/12 VDC side, your batteries, 24 VDC inverter, your 12VDC/120VAC power needs).

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset