newly commissioned Fortress eFlex 5.4 weirdness
From a quick scan of the manual, it could be the one battery with 4x LEDs ON (no flashing)--That battery may not be feeding any current to your loads (all ON is resting fully charged state?). Or it may indicate 76% yp 100% state of charge while discharging...
These batteries need to go through a "configuration" process--And if not, they may not connect to the battery bus?
Do you have a good volt meter you can measure the battery terminal voltages? And do you have an AC+DC Current Clamp DMM so you can see what current is flowing to/from the two batteries?
https://www.solar-electric.com/lib/wind-sun/Fortress_eFlex_installation_manual.pdf
https://www.solar-electric.com/lib/wind-sun/eFlex-Firmware-Update-Guide.pdf
Have you contacted NAWS support yet? I do not work for them--Just help here running the forum (we are all volunteers here)--Many manufactures usually expect their distributors/retailers to provide first level customer support.
Only other thing to check (besides all connections clean and tight, no heating from poor connections or crimps) is that you wire the two batteries properly to ensure proper current sharing (equal wire resistance from chargers/loads to parallel batteries):
The weird thing is that the two paralleled batteries individually appear to deliver the same voltage even though the LEDs suggest they are out of sync. I validated this by briefly turning off each battery and then measuring the voltage of the remaining one. Additionally, the Radian MATE3s shows the same voltage input as the batteries. So other than the LEDs the system appears to be working properly. Very odd. Oh, and after running a bit longer on battery only power, the LEDs now show batteryA=2 while batteryB=3 which proves that batteryB is in fact discharging. When I charge them back up, they both eventually go back to 4 with batteryB getting there faster.
With a BMS, they could estimate State of Charge based on voltage--But (guessing) more likely is they do it by measuring the current flow (Amperes * Time in Hours).
Battery voltage does vary with load/charging current--Although Lithium Ion batteries have much less voltage dependence vs current than Lead Acid.
One member here had to cycle his Li Ion batteries (different brand, I think) to get the BMS values to match up to "actual" State of Charge (BMS originally reported battery empty when only 1/2 AH capacity discharge).
Anyway... You might be the expert here--Especially after working with the support engineers.
I don't want to mislead you--I am not qualified to do much more than read the manuals.
Thanks for listening to my frustration. Here there appears to be a state-of-the-art LiFePO4 battery bank that I'm willing to invest in. Only to be disappointed in having to deal with "growing pains". I trust I will get there eventually. I will keep folks apprised on this thread of my progress (or lack thereof).
Please keep posting your progress with the Fortress batteries. I am just finishing up a new off grid solar system using Fortress E Flex 5.4 batteries.... We can never escape the "learning curve."Home. 30 Kyocera 265 6MCA, FP2-VFX3648 (two FM80 charge controllers, FW-X240 transformer, MATE3, HUB10, FLEXnet DC, two 80A charge
controll breakers, surge protector), Zomeworks (two-UTRF-168) 9 panels on each, 2 fixed pole arrays with 6 panels on each, 24 Rolls Surrettes S-1660 (2 v) for a 48 v battery bank, various MidNite circuit breakers, combiner boxes, Zephyr Power Vent, Hydrovolt, MidNite Solar surge protector for AC/DC circuits. Honda generators; 800, EU2000i, EM3500sx, EM6500. Generac 8000.Off road Jeep trailer M416 conversion. 4 Kyocera 40 watt PV panels, Outback FX 2012 MT, Trimetric 2025 RV, 4 Optima Blue Tops, 400 watt AirX wind turbine (12 v), Morningstar Sunsaver S20 w/LVD disconnect , MidNite battery capacity meter, various fuses,.
NEW 12/21: Sold the Jeep trailer, so that's gone. The Home system is I am redoing completely, retiring the "old" home systems except still using Kyocera solar panels, etc. New permitted system: roughly 16,000 watts of solar panels (54 panels, Kyocera and REC), spread out on 2 Zomeworks, 2 Powerfab pole top mounts, and a large Snap N Rack ground mount (8000 watts with grade beam footings).. 2 Outback 8048A with load centers, 4 Outback flex 100 charge controllers, 4 combiner boxes, multiple surge protectors, Mate 3s, HUB 10, FNDC, 2 Lynx 1000 amp bus bars, 6 Fortress E Flex 5.4 Lithium Batteries, Square D Stu 223 disconnect, lots of matched battery cables, circuit breakers, fuses, etc. Still finishing ground mount, inspector said to finish system and then final, estimate 2-3 weeks, no anticipated problems going well. Kohler 14kW RESA, Honda EM6500, etc.
Identified some Fortress weirdness: Using their CANBUS diagnostic tool, the pair of eFlex batteries are displaying different internal data, even though externally both the SOC LED lights as well as the individual battery voltage appear to be the same for both batteries. NOTE: both batteries have been updated to the latest firmware as shown in the screenshot. Thoughts?
here's what things look like at the combiner.
From your status screen... What does this mean?
Min Cell Volt Num = 5 or 2
I would have guessed that both batteries should have the same "number" (5/2/whatever)? That would seem to be a non-trivial variance (not knowing what the heck it is).
Good catch. I missed that entirely.
I've cycled the batteries a few times now and the SoC LEDs are now in sync. The status screens look "better" too. Even though there are obvious differences in the two (brand new) batteries, Fortress support says based on the latest reports shown below, "all looks well". So I guess I'll have to take them at their word.
- 232 Forum & Website