30 amp connection - too hot baby!
MarkC
Solar Expert Posts: 212 ✭✭✭
I have a 30 amp brkr circuit with 28 amp max current limited (Do I need to reduce the max current to ~ 24 amps to be code compliant?). The L6-30P/R connection point gets very hot (170 oF) in a matter of hours. The plug is a "factory installed" part of a 10 AWG cable. The receptical is a Hubble brand that I installed myself - and have double checked good/tight wire installation. Both "plugs" get very hot - much hotter than the cable (that gets somewhat hot ~130 oF)
Is this normal? Do I need to worry about such temperatures? I've reduced the max current to 22 amps and will "test" again today, however, why would 30 amp rated connectors get so hot?
Is this normal? Do I need to worry about such temperatures? I've reduced the max current to 22 amps and will "test" again today, however, why would 30 amp rated connectors get so hot?
3850 watts - 14 - 275SW SolarWorld Panels, 4000 TL-US SMA Sunny Boy Grid tied inverter. 2760 Watts - 8 - 345XL Solar World Panels, 3000 TL-US SMA Sunny Boy GT inverter. 3000 watts SMA/SPS power. PV "switchable" to MidNite Classic 250ks based charging of Golf cart + spare battery array of 8 - 155 AH 12V Trojans with an APC SMT3000 - 48 volt DC=>120 Volt AC inverter for emergency off-grid. Also, "PriUPS" backup generator with APC SURT6000/SURT003 => 192 volt DC/240 volt split phase AC inverter.
Comments
-
The NEC has one rating for "standard" circuits, and another rating for "continuous use" circuits.
Circuit breakers are rated to trip at 100%+ rated load, and rated to not trip at 80% or less current. In between, the breaker may never trip, trip after hours, or whatever.
I was looking any outlet and cord temperature ratings--And I did not find anything specific. However, for NEC wiring, there are temperature ratings:
https://lugsdirect.com/WireCurrentAmpacitiesNEC-Table-301-16.htm
So--I would start to worry if the insulation was in the 140-194F range... And of course, Ambient temperature affects wiring temperature (cool 70F room vs 95F room in summer sunny conditions)... And cord ratings:Size Copper Conductors Aluminum Conductors
Copper-Clad Conductors60° C
(140° F)75° C
(167° F)90° C
(194° F)60° C
(140° F)75° C
(167° F)90° C
(194° F)AWG
KcmilTypes Types Types Types Types Types TW RHW TBS TW RHW TBS UF THW SA UF THHW SA, SIS THWN SIS THW THHN, THHW XHHW FEP THWN THW-2 USE FEPB XHHW THWN-2 ZW RHH USE RHH, THHN RHW-2 THWN USE-2 XHHW XHH, XHHW XHHW-2, ZW-2
http://www.chem.cmu.edu/groups/bier/procedure_files/general/powercords.pdf
If you wanted to send 30 amps through the plug/cord continuously--Then I would do the 1.25 / 0.80 derating (1/0.80=1.25)- 30 amps * 1.25 NEC continuous derating = 37.5 ~ 40 amp rated branch wiring/circuit breaker suggested.
- 30 amps * 0.80 NEC continuous current derating = 24 amps max continuous load
Say you have a 0.1 Ohm resistance and 30 amps vs 24 amp load:- P = 30a^2 * 0.1 Ohms = 90 Watts heating
- P = 24a^2 * 0.1 Ohms = 57.6 Watts heating
- 24a/30a = 0.80 = 80% (or 20% reduction in current)
- 57.6w/90w = 0.64 = 64% (or 36% reduction in heating)
I have seen a spool of extension cord get pretty hot. The coiled cord/poor air circulation heats the cord vs just laid out straight point to point.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Bill - I set the current on my EVSE at 22 amps and in an hour, the connection temp went to 104 oF - probably about what your calc method would predict. Next try is 24 amps and check - likely where I'll stay. That is plenty of "juice" to charge my Leaf overnight. 240*24= 5760 VA. The on board charger is rated for 6.6kw, so all should be good. Added benifit is that I can probably stay with my 30 amp breaker set.
Thanks for your reply,
Mark3850 watts - 14 - 275SW SolarWorld Panels, 4000 TL-US SMA Sunny Boy Grid tied inverter. 2760 Watts - 8 - 345XL Solar World Panels, 3000 TL-US SMA Sunny Boy GT inverter. 3000 watts SMA/SPS power. PV "switchable" to MidNite Classic 250ks based charging of Golf cart + spare battery array of 8 - 155 AH 12V Trojans with an APC SMT3000 - 48 volt DC=>120 Volt AC inverter for emergency off-grid. Also, "PriUPS" backup generator with APC SURT6000/SURT003 => 192 volt DC/240 volt split phase AC inverter.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed