Battery charger
maas
Registered Users Posts: 1 ✭
Living in the bush in sierra leone. I bought a complete solar system. 4 panels 250watt 4 batteries 200AH 1 hybrid inv 3Kw.
With a 24/7power in the house my 4 panels are not able to charge fully. Resulting in power shutdown in the morning.
Question.
-I have an 220v/ 24v battery charger. May I connect this to the battery bank without interfering with the hybrid charger which will also charge.
-And if so may I adding up the amperage of the seperate systems.
With a 24/7power in the house my 4 panels are not able to charge fully. Resulting in power shutdown in the morning.
Question.
-I have an 220v/ 24v battery charger. May I connect this to the battery bank without interfering with the hybrid charger which will also charge.
-And if so may I adding up the amperage of the seperate systems.
Comments
-
Welcome to the forum Maas,First--Get your batteries charged quickly and fully (assuming they are some sort of Lead Acid chemistry batteries). Lead Acid batteries, if left under ~75% state of charge for days/weeks/months will quickly sulfate and die.Next--I like to talk about a balanced system design that meets your needs/loads. Either design the system to meet your loads, or define how much energy your system can produce per day/by season, then live within the means of the system (and/or use backup power sources such as a genset).Can you tell us more about your battery bank (Lead Acid, GEL, AGM, Li Ion, or what)?The short answer is you can (usually) parallel charging sources to one battery bank. The big things are 1) get the charging voltage settings correct, 2) make sure the charging current from both sources are not too much for the battery bank, 3) I suggest that each charging source be connected to the battery bus directly ("star" wiring) and not from charger A to charger B to battery bank (daisy chain) as the chargers sharing the same cable can confuse each other.More or less--As a warning to everyone reading here--I suggest that for a full time off grid power system--That the inverter be no larger than the solar array. If you have a 1,000 Watts of panels, generally, you would be looking at a 1,000 Watt maximum inverter.Anyway--I will type more--But I am heading out right now.-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
-
1000 watts of panels 1000 watt inverter.
A great and easily understood "rule of thumb".
Thanks for this Bill; makes complete sense.Island cottage solar system with appriximately 2500 watts of panels, 1kw facing southeast 1.3kw facing southwest 170watt ancient Arco's facing due south. All panels in parallel for a 24 volt system. Trace DR1524 MSW inverter which has performed flawlessly since 1994. Outback Flexmax 80 MPPT charge controller four 467A-h AGM batteries. Insignia 11.5 cubic foot electric fridge 1/4hp GSW piston pump. My 31st year. -
Hello again Maas,
I will go through a design assuming you have a 400 AH @ 24 volt flooded cell lead acid battery bank...
First, for a full time off grid home, suggest 2 days of storage and 50% maximum discharge. So, the daily battery bank usage would be (overnight, or 24 hours for a day with poor weather):- 400 AH * 24 volts * 0.85 AC inverter eff * 1/2 days storage * 0.50 max planned discharge = 2,040 WH per day from battery bank
- 2,040 WH per day from battery bank / 5 hours evening usage = 408 Watts average AC load (much less than a 3,000 Watt AC inverter)
- 400 AH * 29.0 volts charging * 1/0.77 solar panel+controller deratings * 0.05 rate of charge = 753 Watt array minimum
- 400 AH * 29.0 volts charging * 1/0.77 solar panel+controller deratings * 0.10 rate of charge = 1,506 Watt array nominal
- 400 AH * 29.0 volts charging * 1/0.77 solar panel+controller deratings * 0.13 rate of charge = 1,958 Watt array "typical" cost effective maximum
http://www.solarelectricityhandbook.com/solar-irradiance.htmlFreetown
(For best year-round performance)
Average Solar Insolation figuresMeasured in kWh/m2/day onto a solar panel set at a 82° angle from vertical:
In general, you are in a very sunny climate... Lets take July as your "break even month" (may need a backup genset for a stretch of cloudy weather).Jan Feb Mar Apr May Jun 6.54
6.76
6.66
6.19
5.48
4.55
Jul Aug Sep Oct Nov Dec 3.76
3.68
4.65
5.47
5.81
6.25
- 2,040 WattHour load * 1/0.52 off grid AC system eff * 1/3.76 hours of sun per day = 1,043 Watt array July "break even"
As it stands right now... Your 400 Watt array in January would supply around:- 400 Watt array * 0.52 off grid AC system eff * 6.54 hours of sun per day = 1,360 Watt*hours per day
Most people overestimate how much energy their solar system can supply, and underestimate their daily loads.
To make "best use" of your present battery system--I would be suggesting a 1,506 to 1,958 Watt array as a good match for your battery bank.However, the 3,000 Watt AC inverter suggests that you are planning on using a lot more than 2,040 WH of power per day, or more than ~408 Watt average loads for 5 hours per day... And your 400 AH @24 volt battery bank would not really (edit/addition - BB) "reliably" support around a 3,000 Watt AC inverter on a lead acid battery bank...Need to make a correction here... A common rule of thumb for a lead acid battery bank is a maximum inverter rating of ~500 Watts per 100 AH @ 24 volt battery bank. In this case a 400 AH @ 24 volt bank would support around a max 2,000 Watt inverter "reliably" (over battery state of charge/age/temperature). AGMs and Li Ion can support higher inverter ratings--But for a standard off grid home, the larger inverters tend to just waste power (tare losses--Using power just being turned on).
Anyway... Lots of questions on my part (daily loads, details on the hybrid inverter/solar charger, etc.). The above is the basic math for your system as currently designed (relatively conservative--Solar panels are "cheap" these days and batteries are expensive--So adding more solar panels to keep the battery bank "happy" will save you money in the long run)...
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
How are you planning on powering the battery charger?
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed