Battery Cable Size
desertsun
Registered Users Posts: 9 ✭✭
We just ordered 8 6v 445AH lead acid batteries for our 48v system. Our old batteries are 400AH and have 2/0 battery cables which were already installed when we bought the house. They are pure copper with tin coated copper lugs. The inverter is a 4.4kw Magnum.
Someone told us the 2/0 size is not the most efficient and we should put smaller wires on. Someone else told us that having that size wires was great. We often get conflicting information about things like this. Can someone explain in layman's terms which size would be best? We could just reuse the existing cables, unless that is not ideal. Thanks in advance.
I am a little confused... 6x 6 volt batteries = 36 volt battery bus. 8x?
- 4,400 Watts * 1/0.85 AC inverter rating * 1/42.2 volts battery cutoff = 123 Amps max continuous
- 123 amps * 1.25 NEC breaker/branch circuit derating = 154 Amp rated circuit/breakers (round up to next available standard sizes)
https://lugsdirect.com/WireCurrentAmpacitiesNEC-Table-301-16.htm
145-195 amps (depending on insulation, temperature, conduit, etc.)...
And if you run 123 amps through 6 feet of 2/0 cable (one way run):
https://www.calculator.net/voltage-drop-calculator.html?material=copper&wiresize=0.2557&voltage=48&phase=dc&noofconductor=1&distance=6&distanceunit=feet&eres=123&x=60&y=19Result
Voltage drop: 0.12
Voltage drop percentage: 0.24%
Voltage at the end: 47.88- 0.12 volts * 123 amps = 15 Watts
- 15 Watts loss / 4,400 Watt loads on inverter = 0.003 = 0.3% DC cable losses
Yes that was a typo, I meant 8 batteries.
Thank you very much! -
between batteries 2/0 is fine......from batteries to inverter is where a larger size might be handy depending on the distance from batteries to inverter
bigger wire = less resistance..less resistance is good....so whoever told you to go to smaller wire...doesnt understand electrical resistance
soooo...reuse those wires
12 panels 6 series 2 parallel 2100 watts, 1 XW60-150 CC, 16 trojan 6V batteries 8 series 2 parallel 450 Ah, 1 XW 6848 pro, 1 5500 watt champion inverter generator( I know...I need a 12Kw )