Parallel Operation in Split Phase
Panapat
Registered Users Posts: 15 ✭✭
I am getting close to installing my 6 kWh off grid system. Its comprised of two 3 kWh multi-functional inverters running in parallel, and two 10 kWh lithium battery packs. This is how they are supposed to be wired. As you can see it doesn't show the neutral tied to ground. But it also has a dry contact on each inverter which ties the neutral to ground via a grounding box whilst on battery power. My question is, as I am totally off the grid can I not tie the neutral to ground in my distribution boxes? Here in Panama we "follow" USA code.
Generally speaking, you wouldn't want a N/G bond in multiple places. If I'm understanding your setup, this would be the case while on battery with bonding done both at the inverters and in the distribution panel.
If the inverters lift the bond when not inverting, you might bond at generator (if not already bonded)?
I don't have a generator. The supplier said I should bond at the first distribution box. The GE panel I am using provides a screw to bond the neutral to the case. The others will remain isolated as you suggested.
I may be misunderstanding. If the inverters are designed to N-G bond on battery power, you wouldn't want a second bond at the disconnect/distribution box as well.
Is it possible the inverter dry contact bonding is or should be disabled in an application with dual inverters? If so, bonding would normally be done at the first disconnect.
Do you have a link to the inverter?Off-grid.
I don't have a link to the manual but this is what it says about Neutral and Ground using the dry contact. Engineers say that I can disable the dry contact, which is the default, and ground at the house box as you suggest.